What types of testing in 11Kv Ht switchgeat during testing?
Answer Posted / pillay
I belive you mean commisioning tests.
some of them are,
A)INSULATION TEST
b)contact resistance test
c)HV holding test
d)primary and sec injection test on the protection cct
e)transformers insulation, ratio test,vector group, insulating
oils dielectric tests.
f)cables insulation, phasing test
| Is This Answer Correct ? | 11 Yes | 4 No |
Post New Answer View All Answers
why 15 kw motor winding resistance is low then 5 kw motor winding resistance?
Explain about technical and non technical losses in distribution system?
what is parellel power factor correction?
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
DESCRIBEPNEUMATIC SYSTM OF ASH HANDLING PLANT
Explain the following and how these are working with PLC Unit 1 I/O Module Card 2 Adaptor Card 3 Ribbon Adaptor 4 I/O bus 5 I/O Devices
what is the excess air in furnace
For RCD (Residual current device) Icu is defined. How i can find Ics for them?
What are the commonly used schemes for the bus zone protection?
sir my exam is on 19/6/2013 under electrical branch pls send me sample aptitude questions as well as sample technical questions for jindal steel and power company
how to remover corona effect and hysteresis losses from contactor
how we can calculate power factor in single phase & three phase ?thank u
What is the formula to calculate distribution transformer De-rating on iron losses basis
what is POTT and PUTT explain?
what is fault level of power system ?