What types of testing in 11Kv Ht switchgeat during testing?
Answer Posted / mriganka das
Transformer:
1)IR Test
2)Magnetising Current Test
3)Magnetic Core Balance Test
4)Vector Group Test
5)Ratio Test
6)Polarity Test
7)Oil Test (DGA,Dielectric Strength,Moisture content)
8)RLA test (Dirana, Thuran)
Current Transformer :
1) Ratio Test
2) IR Value Tset
3) Polarity Test
4) Knee Voltage Check
5) Winding Resistance Test
6) Back to Back Test
7) Tan Delta Test
8) High Voltage Test
Breacker Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
Isolator Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
5) Hot point Check ( in running condition)
| Is This Answer Correct ? | 7 Yes | 1 No |
Post New Answer View All Answers
can you send me the placement papers of electrical engg. from companis like NTPC,DRDO,IOCL,HPCL,BPCL etc.?If,plz send as soon as possible.Thanks.
Batteries. What is the difference between Lead and Nickel batteries ?
What is the role of Dedicated earthing in UPS System?
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB to another Power DB?
What is step signal?
how to set relay setting? and example calculation...
sir i am apearing for nic exam.i dont know exam pattern.can you please send me some model papers
i need mat lab program to find out the transmission line losses,regulation and losses
STATE USE OF ARC RUNNERS & SPLITTERS ?
how indusrial diesel generator work
please tell me, how i clear the objective test? when i studied form the one book after i solved the objective ,that time i solved that qes. but if i tried solve objective form the other book then i could not solved these que.
WHY DO VOLTAGE TRANSFORMERS FAIL DURING EARTH FAULT IN THE DELTA CONNECTED 6.6KV ELECTRICAL SYSTEM
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
list the advantages of RCCB over other circuit breakers?
At what factor resistance r of a conductor depends?