Why CT secondary should not be kept open?
Answers were Sorted based on User's Feedback
Answer / ashok bhatnagar
CTs are used for the measurement of high currents as a
primary sensor. The output of the CT is normally connected
to the relevant ammeter which has very low impendence and
secondary remains almost short circuited. The secondary
current has no control over primary current in a CT. If
secondary is open circuited two things will happen :
1. Due to absence of secondary current no counter magnetic
field is produced and flux in core of CT rises to
saturation level which can change the charateristics of CT
and damage it permanently
2. since number of turns in secondary is very high (1:
1000) for , a very high voltage may be induced in secondary
that can harm the prsons working on the instruments panel.
Is This Answer Correct ? | 308 Yes | 27 No |
Answer / arvind chalka
if secondary is open then secondary current and flux will be zero. so that total flux is increased.
emf is directly proportional to flux than there will be induced a high voltage that saturate the core and demage the transformer.........thus we should not be open secondary .
Is This Answer Correct ? | 89 Yes | 9 No |
Answer / achint rajput
A current transformer should never be open-circuited while
main current is passing through the primary winding. If the
load is removed from the secondary winding while the main
circuit current is flowing, most of the primary winding
current becomes magnetizing current, but the vector angles
change in such a way as to keep the total current in the
primary the same as before. Because the main circuit is now
mostly magnetizing current, the flux in the core shoots up
to a high level and a very high voltage appears across the
secondary. Due to the high turn ratio usually found in these
transformers, the voltage in this condition can reach a
dangerously high level, which can break down the insulation.
It also becomes a hazard to personnel. The high flux can
saturate the core and result in strong residual magnetism
left in the core, thereby increasing magnetization current
and introducing error in the transformation ratio. One has
to put a short on the secondary winding before removing the
connections.
Is This Answer Correct ? | 27 Yes | 5 No |
Answer / iamdon
The CT secondary should not be left opened secondary due to
following reasons:
1)Zero current in secondary leads zero back emf.So primary
current becomes very high as the primary resistance is very
low.Large heat generated may burn the winding and core.If
the transformer sustain this heat, even then its operation
becomes improper as explained below.
2)CT is bascially a step up transformer.So high voltage
induced in secondary may saturate the core (core becomes
permanently damaged).So the operating point advances in non
linear region,which makes the transformer operation improper
(secomdary current will not replicate the primary according
to the turn ratio).
3)High voltage spikes(order of kV) produced in secondary side
may endanger the life of personnel working on the secondary
side.
4)High voltage spikes(order of kV) produced in secondary side
is sufficient to break down the transformer insulation.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 30 Yes | 19 No |
Answer / rites
CTs are used for in the measurement of current as a primary
sensor. The output of the CT is connected to the relevant
power meter. For CT the primary is the busbar / cable
caarying current which generates current in the secondary
by induction. Now if CT secondary is kept open and current
flows through primary the induced emf in the secondary will
not have a close path to flow which will lead to opening /
bursting of the CT.
Is This Answer Correct ? | 38 Yes | 29 No |
Answer / seema
If we kept the secondary of current transformer open, current in the secondary side will be zero, voltage get increased so it will worked as a VT. At the primary side current is maximum so maximum flux will get inducced in the primary side & zero in the secondary side.so, in that case the difference between the primary flux & secondary flux will be more so the counter balance between that 2 flux is impossible.Result will be increased in primary current, increased in core losses.
Is This Answer Correct ? | 6 Yes | 6 No |
In the physical construction of CTs you can see the secondary
is made up of a winding but the secondary is just one cable or
busbar.So it acts as a step up transtrofmer when the secondary
is left open.It is real I have seen two people who have had their hands burnt due to careless handling of the CTs.
Is This Answer Correct ? | 12 Yes | 33 No |
a motor's measured current is 45amp,whereas the rated current is 38 amps but still it is running ,how?
i want to know how to determine that a surge arrester work properly in 11kv system. and how to test a 12kv surge arrester
what is the equation of insulating resistance of motor???
how to calculate slip ring induction motor stator and rotor currents??
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
Battery is a voltage source? give one example of current source and why?
I have 3 1000 kva single phase transformers and I wish to replace them with one three phase transformer. What is he kva rating of the new three phase, is it 1000 kva also or 3000 kva.
is high voltage or high current is danger
WHAT IS B & C CLASS SURGE PROTECTION AND WHAT IS DIFFERENCE BETWEEN B & c CLASS SP
HOW SKIN EFFECT REDUCE THE CROSS SECTION OF THE CONDUCTOR
WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR
why crgo core is used in transformers?