Answer / tulasidhar
Transformer rating is KVA Instead of KW.bcoz P.f is does not depend.
Is This Answer Correct ? | 27 Yes | 3 No |
Answer / satish r chude
cupper lose dependance upen the voltage and iron lose
depend upen the current. the total tx lose in volt and
current volt amper.VA.
Is This Answer Correct ? | 21 Yes | 2 No |
Answer / loboreliance2003
S(kVA)=P(kW)+jQ(kVAr) where S is total power, P is active
power (Power uses by a resistive load E.g:light, heater,
etc) & Q is reactive power (Power causes by an inductive
load E.g: Induction motor). For a load, we only wants to
know how much work it will do, so information of kW is
enough. However, for a transformer as it has to supply
power to the whole system, it will be affected by both
active & reactive power. So you will have to concern about
the total kVA of your system to choose the correct
transformer. If you only concern about the active power the
transformer can handle and not about the reactive power,
the total power of your system sometimes will be larger
than the total power of the transformer and will damage it.
Is This Answer Correct ? | 8 Yes | 1 No |
kVA is the unit for apparent power. Apparent power consists
of active and reactive power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again.
It occurs when on account of some inertia in the system
there is a phase shift between voltage and current. This
means that the current does not change polarity synchronous
with the voltage. But the heat generated in a winding as
well as the eddy current losses generated in a transformer
core depend on the current only regardless of whether it
aligns with the voltage or not.
Therefore the heat is always proportional to the square of
the current amplitude irrespective of the phase angle (the
shift between voltage and current). So a transformer has to
be rated in KVA.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / m.omar javaid
Its rating is in kva since it does'nt involve any phase
difference b/w v and i i.e pf independent.manufacturers do
not take into account what type of load is to be
connected ,it could either be resistive or reactive.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / pushpendra
Due to losses in transformer ,Because Full load loss(copper
loss)in term of current & No load loss(iron loss)is in term
of vollage .
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sankar maiti(b.tech ee)
cupper lose dependance upen the voltage and iron lose
depend upen the current. the total tx lose in volt and
current volt amper.VA.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sadik pasha
copper losses depends on current and iron losses depends on
voltage so efficency of t/f depends on these two losses so
t/f's rated in KVA.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jey
Transformers and Generators are rated in KVA bcoz PF cannot be calculated( Cu loss depends on Voltage & Iron loss depends on Current). Always the Source end i.e transformer , Generator, power factor cannot be calculated and it is rated as KVA and Destination end i.e is Utility side such as Motor are rated as KW
Is This Answer Correct ? | 0 Yes | 0 No |
How to calculate unit consumption on the basis of load. kWH=kwXhrs.is it correct? kw is motor load.What is unit consumption at 100% load, 50% load & on no load.
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
What are the factors considered for the selection of cable?
Explain the working principle of Synchronous Generator and Assynchronous generator?
can u please mail me the syllabus for GET exam for damodar valley corporation?
in transformers for ex. 100mva and 400kv the secondary current is about 420 amps but for selection of bushing the capacity of selected bushing is 2000A why there is such big difference ?
what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker
why are installed water leakage detection system data centers & server rooms
How to calculate the Short Circuit Impedance in Transformer?
What is the maximum and minimum rating of UPS?
What is the difference between ARC & SPARK?
What is the reason behind current flow(20 A) in amain earth cable of an SMDB? Is cuurent flow(45A etc) through a neutral cable acceptable?