In power point wiring,often,we use less size of earth wire
compared to phase & neutral wire and we use big size pin in
pug top. how is it justified? can we use small size cable
for earthing?
Answers were Sorted based on User's Feedback
Answer / santosh kawade
We use big size pin and socket for power point to reduce
resistance in earth pat and to alway connect earthing first
to equipment before connecting mains and neutal in system.
Using low size cable for earthing in single phase can not
be justified, we have to use same size cable for neutral,
eathing and mains.
In three phase we can use lower size cable for earthing and
neutral.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / j@ru ( sati)
as we know from R =pl\A bigger the size of area lesser the
resistance of conductor...so b using this concept earth pin
provides less resistance to leakage current compared to
other two pin hence leakage current by pass to earth without
damagng appliances..
thats all thank you
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shanmugam annamalai
The reason of earth point in bigger than that others to
save the equipments from leakage current. It means, the
system will be earthed before connecting to the power
supply. Ultimately, if there is any leakage current, it
would bypassed through earth so equipment will be safe.
Please reply, It you need more clarifications
| Is This Answer Correct ? | 4 Yes | 2 No |
What are the different power system losses and how can it be eliminated?
What is transformer tap changers please explain
3 Answers Feedback Venture, Sail,
What is mason's gain formula?
why co incidence factor considered in transformer sizing?
-How do you select cable size for a given load at a given distance from source of supply. How do you find voltage drop.
A mass of 1200g is accelerated at 200 cm/s2by a force. The value of the force required is:(a) 2.4N(b) 2400N(c) 240 kN(d) 0.24N
There is 3phase power cable from 1 point to the other point which is 100m away. Two point equipped with power meter and recorded 1st point is 205kW while the 2nd is 202kW and each phase average carry 400amps. To calculate the resistance of the 3phase power cable, is the formula using will be P=I2R?
what is skin effect
Write down the name of 2 lady Bir Pratin of Bangladesh
in the case of 6.6kv motor starter combination contain fuses on it VCB. but in 11KV motor starter combination Fuses are not using in it's VCB why?
Can we convert off load tap changer transformer to on load tap changer transformer
what is diff. b/w of earth & neutral?. why we are separately using ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)