Why breakers not synchronized when the synchroscope is going
in the anticlockwise direction?
Answers were Sorted based on User's Feedback
Answer / yogesh
If the synchronoscope reads in anticlockwise direction
means the generator is running too slow. To close the
Breaker the incoming Generator frequency should be higher
than the existing Generator. Than only the incoming
Generator will take the load as soon as the Breaker gets
synchronised
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / k.prakashchandra
The power required to run at synch speed will be drawn from
the system.
Is This Answer Correct ? | 0 Yes | 0 No |