I am an electrical power engineer and arranged power system
for a data center, I installed MCB, ELCB and erthing system
TN-C-S.
But some times several ELCBs Disconnect circuits at the
same time! what may be the reason? (the ELCBs are 25A ,30mA)
Answers were Sorted based on User's Feedback
Answer / chandra
Mr. Mehdi, Do check the neutral of all circuits wether they
are connected to same ELCB group. If one neutral from one
group is connected to other group this problem will occur.
Even though all neutral is common at final point, each
neutral will have to pass through the ELCB in order to
monitor the return cuurent.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / prashant
that means tgat u wer using those 30 mA ELCB to feed ur ac/
power sockets or some other heavier load
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.p.sharma
Mr.chandra & mehndi is right and the normally mA of ELCB
used IS AS BELOW:-
1. FOR DOMESTIC = 30MA
2. FOR COMMERCIAL BUILDINGS ETC = 100MA
3. FOR INDUSTRIES = 300MA
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nageshwaran.n
Hi boss, check the connections properly.
Check for:
1. Total Load on MCB's. It should not exceed the market
rating.
2. For ELCB's, check the circuit for the leads interchange.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / mehdi
there wasn't any Falctuation in cicuits. it is strange that
if any problem occured in one circuit others may not be
failed!
I solved my problem by replacing those ELCB with 300 mA
Type!
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pillay
the choice of 30 ma is correct,
or in fact we should be able to
decide what ma rating we want
to choose where.
It could be the fault current was
quite big but fault current could
not be grounded fast enough resulting
in the current floating into other
neighbouring cct resulting in triggering
of the elcb,s.The other solution would
be checking the grounding connections from
the earth pit to upwards and also the actual
earth resistance measurements.
| Is This Answer Correct ? | 0 Yes | 0 No |
Dear Mahdi
Some Current is leakege in earth form circuit and
equepment . so your ELCB was trip.so frist check the all
circuit .
you are using TN-C-S earthing .in this common earth use
for nutral and grounding .
I suggested you for use TN-S type earthing .
| Is This Answer Correct ? | 0 Yes | 1 No |
ELCBs Disconnect circuits at the power fluctuation time or
any other reason????
| Is This Answer Correct ? | 0 Yes | 2 No |
what is meant by bus bar and outgoing/incoming breaker in an electrical/electronic circuit
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?
why transformer are rated in kva.
How to convert KW to KVA or KVAR OR kvar/kva to kw?
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
how much power consumed by 1.5 ton capacity split A.C in 1 hour
how to work exciter in 10 MW alternator?
What is the difference between air & vaccum circuit breakers?
HOW TO IDENTIFY THE RELAYS WHICH APPLICATION IN WHICH RELAY USING
WHY POLARITY TEST OF CT IS VERY IMPORTANT IN SWITCHGEAR
IS diode and blocking diode are the same?..what is meant by blocking diode
why voltage swells and dips???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)