Answer / chandra
Mr. Mehdi, Do check the neutral of all circuits wether they
are connected to same ELCB group. If one neutral from one
group is connected to other group this problem will occur.
Even though all neutral is common at final point, each
neutral will have to pass through the ELCB in order to
monitor the return cuurent.
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / prashant
that means tgat u wer using those 30 mA ELCB to feed ur ac/
power sockets or some other heavier load
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.p.sharma
Mr.chandra & mehndi is right and the normally mA of ELCB
used IS AS BELOW:-
1. FOR DOMESTIC = 30MA
2. FOR COMMERCIAL BUILDINGS ETC = 100MA
3. FOR INDUSTRIES = 300MA
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nageshwaran.n
Hi boss, check the connections properly.
Check for:
1. Total Load on MCB's. It should not exceed the market
rating.
2. For ELCB's, check the circuit for the leads interchange.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / mehdi
there wasn't any Falctuation in cicuits. it is strange that
if any problem occured in one circuit others may not be
failed!
I solved my problem by replacing those ELCB with 300 mA
Type!
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pillay
the choice of 30 ma is correct,
or in fact we should be able to
decide what ma rating we want
to choose where.
It could be the fault current was
quite big but fault current could
not be grounded fast enough resulting
in the current floating into other
neighbouring cct resulting in triggering
of the elcb,s.The other solution would
be checking the grounding connections from
the earth pit to upwards and also the actual
earth resistance measurements.
Is This Answer Correct ? | 0 Yes | 0 No |
Dear Mahdi
Some Current is leakege in earth form circuit and
equepment . so your ELCB was trip.so frist check the all
circuit .
you are using TN-C-S earthing .in this common earth use
for nutral and grounding .
I suggested you for use TN-S type earthing .
Is This Answer Correct ? | 0 Yes | 1 No |
ELCBs Disconnect circuits at the power fluctuation time or
any other reason????
Is This Answer Correct ? | 0 Yes | 2 No |
What are protection of power transformer?
what is the use of Reactive power in power system?
Distinguish between neutral earthing and equipment earthing?
what is linear elements
How to calculate the phase to phase clearness of HT /// LT bus bar?????
How open delta used for protection?
What is Form factor?
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
why we do 2 types of earthing on tranformer ie:body earthing & nutral earthing , what is function. i am going to instal a 5oo kva tranformer & 380 kva DG set what should the earthing value
8 Answers Altrion Technologies,
What is the difference between Class PX & Class X CT's
In any Industry, Which voltage level either 3.3kV or 6.6KV to be chosen? Then I would like to know ,Is there any cost consideration or Rating of motor?
what maximum range of star & delta in hp or kw ?
0 Answers Makkah Hilton Towers,