WHAT IS THE SIGNIFICANCE OF VECTOR GROUPS IN TRANSFORMER?
WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN
TRANSFORMER?
Answers were Sorted based on User's Feedback
Answer / jagadisha
The vector group is used to know the type of winding in
Transformer.First letter in the vector group indicates
primary winding(neutral is indicated if present) and the
second letter indicate secondary winding and next letter is
indicate phase difference between primary and secondary..
let us consider vector group Dyn11-It is most coomon 3-PH
connection,ie Delta is on primary and Star on sec with phase
displacement of 30deg
| Is This Answer Correct ? | 19 Yes | 10 No |
Answer / bijay
well things are explained well above.
i wud like to add something
WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN
TRANSFORMER ?
Ans:-First thing under an abnormal condition(during fault)
the neutral point of trafo rised above the ground potential
and attains a positive potential,hence a current will flow
through the trafo neutral to the ground (mostly the trafo
neutral is earthed with or without a NGR.
As a whole the bottom line is trafo neutral will rise to a
potential which is not desired,protection against the same
is designed,which cut of the supply it this condition
prevails for a longer time( this time is descided at the
time of designing the system.
| Is This Answer Correct ? | 13 Yes | 6 No |
Answer / sunil ulange hit nidasoshi
Vector Groups are made especially to make out difference in
the connections. The connection can be delta(D) or star(Y)
The primary winding connection always denoted by Capital
Letter (D), and secondary winding connection always denoted
as small letter (y), and neutral n
The number after that indicates the phase difference
between the primary and the secondary voltage.
e.g.-> DYn11 means transformer is star connected with
secondary voltage leading the delta connected primary
voltage by 30 degrees.
normally distribution transformers are have Dyn11 connection
because secondary of transformer are connected to at user
end means motors,inductive load etc,
These loads always havelagging Power factor thatswhy Dyn11
connected transformer means secondary volatage leads by
primry voltage by 30 degrees, hence Power factor maintened
constant.
In Clock 11 indicates angle between 12 & 11 is 30 degrees
i.e. 360/12=30 degree
Sunil ulange
Application Engineer
Southern power equpment Limited bangalore
any Questions @ sunil_031@yahoo.com
| Is This Answer Correct ? | 16 Yes | 11 No |
Answer / poonam
Vector Groups are made especially to make out difference in
the connections. The connection can be delta(D) or star(Y)
The number after that indicates the phase difference
between the primary and the secondary voltage.
e.g.-> Y11 means transformer is star connected with
secondary voltage leading the primary voltage by 30 degrees.
I am not sure of the effect of phase displacement in
transformer
| Is This Answer Correct ? | 16 Yes | 12 No |
Answer / geno peter
well , significance of vector group depends upon the load
of the transformer. if phase displacement changes then the
connections in the transformer or tap switch of the
transformer has some problems
| Is This Answer Correct ? | 2 Yes | 7 No |
if dc motor can operate by ac supply ? if its possible means how ?
what is the carona effects meaning in HT line transmmission system
what is ripple component in ac supply?
why dimmerstate always connected in star connection? what will happen if it connected in delta?
what can i do line to line fault
what is allowable current flows from phase to ground with out tripping the breaker
can we use 3 phase UPS for Motors and Other Machines
how can we save enegry by using VFD for Resiprocating Air compressor which is having more unloading running hours
what is the meaning of 5% droop or 7% droop in AVR?
when u are given a timer,push buttons and contactor, how do i practically make a star delta control circuit and a direct online control circuit?
1. alternator has full load regulation of 4% when pf of the load is 0.8 lag, 1500 rpm. full load regulation of 1400 rpm for 0.8lag will be ________ ?? 2. torque angle of a sync m/c operating from a constt voltage bus is usually defined as space angle between _______ . 3. method most effective in finding out no load losses in large DC shunt motoris ______ . 4. current carrying capacity of fuse material depends on ______ . 5. coil has res. 10 ohm, inductance 1H. what wil be current after 0.1sec after switching on to a 500V DC SUPPL ? ? 6. effect of phase lag compensation on servo systems ___________ . 7. rotor of a dc machine is usually supported upon ______ . 8. DC motor is preferred to AC motor in which application ?? 9. 3 nos of 10:1 Xmer are connected in Star-Delta to supply a load at 230V.the supply voltage must be ______ . 10. voltage source produces max current in which circuit. 11. cal. power, if current and voltage are out of phase by 90 degree. 12. suitable length of Xmission line of power at 66 KV. 13. Which of the theorm helps in simple computation when the load across a ckt is varying ?? 14. what is the adopted line length for power Xmission of power by cables ??
What is the difference between Dielectric and Insulator
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)