If we connect the capacitor banks for DG set for maintainig
the power factor, it will effect to alternator
windings??????????
Answers were Sorted based on User's Feedback
Answer / gaurav khanduja
we will not have to connect the capacitor with the D.G.
because D.G. work on the principle of AVR(Automatic voltage
regulator)and AVR work always lagging PF. if we connect the
capacitor then it gives leading P.F.And O/P voltage of D.G.
will be vary so we never connect the Capacitor with the D.G.
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / mushtaq
Capacitors can be connected to DG set But, the Power factor should be always maintained below Unity (i.e lag), if it cross beyond the Unity (i.e lead) Alternator's Automatic voltage Regulator get burnt and simultaneously the windings
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pradeep kumar dhar
You can connect capacitors across load to the extent the
reactive power is compensated.Over compensation is
harmful.As a thumb rule 80% compensation is o.k.But then
the voltage should not be allowed to increase beyond limits.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / indrajeet
We can connect capacitors to compnsate reactive power to a
certain limit because in DG set there will not any value
for shooting of Max. demand.One benifit you will get that
your alternator winding will get more life.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / pradeep dhar
The generator is a source of power.You never connect
capacitor across source.The capacitor should be connected
accros load for power factor compensation so as to meet the
reactive power demand.overcompensation is harmful.
| Is This Answer Correct ? | 0 Yes | 1 No |
how to calculate differential current when we testing differential relay..suppose we have 1000kw generator,630amp VCB,what value we should put /inject so that relay trip the VCB? PLLZ justify ur comment
what transformer we used normally and upto which kva?
I need to calculate the Battery bank back up for below configuration:- UPS - 120 KVA Battery Bank - 200Ah Volt of each cell - 12 V Total No of cell - 34 No's Can you please help me to get the battery back up time for above configuration...? along with formula
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
in my working site. momentary jerck in electrical supply ocurred frequently which cause of multiple losses in our electrical equipements. how can we protect our electrical machines and equipements in this situation.
As we know that during saturation test of CT from secondary side, the current in secondary shoots up after core saturation. How core saturation effects the secondary current?
How calculate the MTA in relay?
difference between microprocesser and microcontroler
I have iti elec, 1st aid, and 5 yrs experience in 7.5 mw power plant. Am i eligeble for 11kv license in telangana state..when, how to apply for that.?
why the measure taken in multiplication factor of 11for voltage like.. 110V,220V,440V,1.1KV,6.6KV,11KV,33KV,66KV,110KV,132KV,220KV
in thermal power plants by opening the turbine governor valve increase the generator load. how
megger how much voltage will produce ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)