If we connect the capacitor banks for DG set for maintainig
the power factor, it will effect to alternator
windings??????????
Answers were Sorted based on User's Feedback
Answer / gaurav khanduja
we will not have to connect the capacitor with the D.G.
because D.G. work on the principle of AVR(Automatic voltage
regulator)and AVR work always lagging PF. if we connect the
capacitor then it gives leading P.F.And O/P voltage of D.G.
will be vary so we never connect the Capacitor with the D.G.
Is This Answer Correct ? | 15 Yes | 0 No |
Answer / mushtaq
Capacitors can be connected to DG set But, the Power factor should be always maintained below Unity (i.e lag), if it cross beyond the Unity (i.e lead) Alternator's Automatic voltage Regulator get burnt and simultaneously the windings
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pradeep kumar dhar
You can connect capacitors across load to the extent the
reactive power is compensated.Over compensation is
harmful.As a thumb rule 80% compensation is o.k.But then
the voltage should not be allowed to increase beyond limits.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / indrajeet
We can connect capacitors to compnsate reactive power to a
certain limit because in DG set there will not any value
for shooting of Max. demand.One benifit you will get that
your alternator winding will get more life.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / pradeep dhar
The generator is a source of power.You never connect
capacitor across source.The capacitor should be connected
accros load for power factor compensation so as to meet the
reactive power demand.overcompensation is harmful.
Is This Answer Correct ? | 0 Yes | 1 No |
Why frame of the motor is specified?. If we mention KW and voltage level,automatically frame is decided or separately frame is compulsory to mention?.
how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula
What is the PI test stand for transformer and what is the producer to do this test?
what can i do line to line fault
Purpose of providing neutral isolation panel for parallel operation of diesel generator
-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.
what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure
Which type of transformer used in lighting load?
sir, why alternator output is connected to delta side in to generating transformer? any reasion?
Hai, I am from EEE branch.On feb 17 iam going to write an Exam for hindustan petrolium corporation Ltd.So plz send me the written exam pattern/Q's/interview questions.please mail to yuva_polisetti@yahoo.co.in
1 Kva = How many KW
What is the different type of class in CTS and why it is required