If we connect the capacitor banks for DG set for maintainig
the power factor, it will effect to alternator
windings??????????
Answers were Sorted based on User's Feedback
Answer / gaurav khanduja
we will not have to connect the capacitor with the D.G.
because D.G. work on the principle of AVR(Automatic voltage
regulator)and AVR work always lagging PF. if we connect the
capacitor then it gives leading P.F.And O/P voltage of D.G.
will be vary so we never connect the Capacitor with the D.G.
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / mushtaq
Capacitors can be connected to DG set But, the Power factor should be always maintained below Unity (i.e lag), if it cross beyond the Unity (i.e lead) Alternator's Automatic voltage Regulator get burnt and simultaneously the windings
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pradeep kumar dhar
You can connect capacitors across load to the extent the
reactive power is compensated.Over compensation is
harmful.As a thumb rule 80% compensation is o.k.But then
the voltage should not be allowed to increase beyond limits.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / indrajeet
We can connect capacitors to compnsate reactive power to a
certain limit because in DG set there will not any value
for shooting of Max. demand.One benifit you will get that
your alternator winding will get more life.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / pradeep dhar
The generator is a source of power.You never connect
capacitor across source.The capacitor should be connected
accros load for power factor compensation so as to meet the
reactive power demand.overcompensation is harmful.
| Is This Answer Correct ? | 0 Yes | 1 No |
Hi guys! Plz help me to answer the following questions. 1. What are the types of transmission line energy losses? 2. Why are the VLF are used some types of services? 3. What frequencies are used for reliable beyond the horizon terrestrial communication without repeaters? 4. To permit selection of 1 out 16 equi-probable, what is the number of bitis required? 5. What is the most common modulation used for telegraphy? 6. What is the multiplexing is used to increase the capacity of the optic fiber? Thanks
what is the difference betn earthed and unearthed cables which is commanly used why?
What are the various methods for effecive earthing in a factory in a rocky terrain, where soil resistivity is extraordinarily high? The usual method of 3 m deep earth pits is not serving the purpose.
WHAT IS DIFFERENCE BETWEEN PHASE CONVERTER AND VFD
In which connection the voltage will be more , in star or delta connected motor?
What is the Power factor of DC Power system ?
HOW EFFICIENTLY LOAD IS SHARED BETWEEN ALTERNATORS
need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.
what is the difference between neutral and earth????
Star & delta kis principale pa hai.
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
What is the rate of WCT on the Electrical Contracts comprising of DG Sets and Civil Works in Delhi ?
0 Answers MES Military Engineer Services,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)