Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


If we connect the capacitor banks for DG set for maintainig
the power factor, it will effect to alternator
windings??????????

Answers were Sorted based on User's Feedback



If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to al..

Answer / gaurav khanduja

we will not have to connect the capacitor with the D.G.
because D.G. work on the principle of AVR(Automatic voltage
regulator)and AVR work always lagging PF. if we connect the
capacitor then it gives leading P.F.And O/P voltage of D.G.
will be vary so we never connect the Capacitor with the D.G.

Is This Answer Correct ?    15 Yes 0 No

If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to al..

Answer / mushtaq

Capacitors can be connected to DG set But, the Power factor should be always maintained below Unity (i.e lag), if it cross beyond the Unity (i.e lead) Alternator's Automatic voltage Regulator get burnt and simultaneously the windings

Is This Answer Correct ?    3 Yes 0 No

If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to al..

Answer / pradeep kumar dhar

You can connect capacitors across load to the extent the
reactive power is compensated.Over compensation is
harmful.As a thumb rule 80% compensation is o.k.But then
the voltage should not be allowed to increase beyond limits.

Is This Answer Correct ?    4 Yes 2 No

If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to al..

Answer / indrajeet

We can connect capacitors to compnsate reactive power to a
certain limit because in DG set there will not any value
for shooting of Max. demand.One benifit you will get that
your alternator winding will get more life.

Is This Answer Correct ?    1 Yes 2 No

If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to al..

Answer / pradeep dhar

The generator is a source of power.You never connect
capacitor across source.The capacitor should be connected
accros load for power factor compensation so as to meet the
reactive power demand.overcompensation is harmful.

Is This Answer Correct ?    0 Yes 1 No

If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to al..

Answer / vishwas darne

I am also not sure

Is This Answer Correct ?    0 Yes 2 No

If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to al..

Answer / stanley

The cable between terminal to capacitor will burn if we
connect additional (external) capcitor.

Is This Answer Correct ?    5 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

Hi guys! Plz help me to answer the following questions. 1. What are the types of transmission line energy losses? 2. Why are the VLF are used some types of services? 3. What frequencies are used for reliable beyond the horizon terrestrial communication without repeaters? 4. To permit selection of 1 out 16 equi-probable, what is the number of bitis required? 5. What is the most common modulation used for telegraphy? 6. What is the multiplexing is used to increase the capacity of the optic fiber? Thanks

0 Answers  


what is the difference betn earthed and unearthed cables which is commanly used why?

2 Answers   Bhel, Power Grid,


What are the various methods for effecive earthing in a factory in a rocky terrain, where soil resistivity is extraordinarily high? The usual method of 3 m deep earth pits is not serving the purpose.

4 Answers  


WHAT IS DIFFERENCE BETWEEN PHASE CONVERTER AND VFD

1 Answers  


In which connection the voltage will be more , in star or delta connected motor?

3 Answers  


What is the Power factor of DC Power system ?

9 Answers  


HOW EFFICIENTLY LOAD IS SHARED BETWEEN ALTERNATORS

1 Answers  


need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.

0 Answers  


what is the difference between neutral and earth????

4 Answers  


Star & delta kis principale pa hai.

3 Answers   ME,


Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.

0 Answers   Piramal Healthcare,


What is the rate of WCT on the Electrical Contracts comprising of DG Sets and Civil Works in Delhi ?

0 Answers   MES Military Engineer Services,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)