We have a 12MW power plant & we inject 5-6MW power to
Orissa GRID. For this we have a 33KV/11KV switch yard
having 12.5MVA power transformer. Some times we draw power
during emergency. It is observed that during Export or
Import for load less than 500Kw the power factor is
decreasing to 0.3 . This is happening only during export or
import. During island condition TG power factor OK.Our
capacitor bank is provided with our Power plant auxilliary
load. Please suggest how I can we improve our power factor
during low load (GRID).
Answers were Sorted based on User's Feedback
Answer / velusamy
This problem can be solved by switching off all capacitor
banks during low load. we have faced Similar type of
problem in our cement plant loads which are fluctuating in
nature which causes export / import of power fluctuation(
loads go +500kw and - 500kw withing 1 or two seconds).
The main reason for this low power factor is due to
reactive power consumption of your 12.5 MVA power
transformer.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / s.balasubramanian
If you can furnish me the scheme used by you for import
export ontrol I will be able to review
balasubramanian
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
During export, it may be possible to improve pf with
excitation.The low pf may also be attributed to erroneous
measurement by CT's at very low loads.Tr may also contribute
to low pf to some extent depending on positions of pf meter
and capacitor bank .
| Is This Answer Correct ? | 0 Yes | 0 No |
I have 380.KVA DG set how to Calculate the units from DG.
2 Answers Ozone Pharma, Sperry Plast Limited, Sterling,
How to calculate Temp from Resister from PT100 equation,
please design a rectifier with batteries for below requirement and also explain how you calculate this solution, Load = 700Amp DC Backup time = 6 hour. please explain briefly ?????
If 11 KV breaker on the primary side of a 11 KV/3.3 KV 12.5 MVA transformer can be installed at a distance of 1000 mtrs through a 11 KV cable. If no what are the probable reasons.
After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.
if its possible for step up or step down DC volage directly ? possible means how we can do it ?
which type of capacitors using in single phase motors
What are the applications that use Solid State Drives in your home?
what is the terminal voltage of dc series generator running at rated speed at no load?
WORKING PRINCIPLE OF VACCUM CKT BREAKER ?
why is fan rotating slow speed, what is the problem?
power inverter we are using 2n3773 power transister in that places we can use any IGBT ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)