What is Black-out and Brown-out situation in the context of
voltage stability in power system?
Answer / iamdon
Black-out:
Sequence of events following the voltage instability
leading to very low voltage or almost no voltage in a
significant part of the system.This is a natural phenomenon.
Brown-out:
Reduction made in voltage at load end to reduce power
demand so that the Black-out situation can be averted.This
is done artificially.With the reduction in voltage, power
flowing through transmission line reduces.This avoids the
cascade tripping of heavily loaded lines.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 4 Yes | 0 No |
what is Thermocouple? Type of its.
What is delta stare switch?
Energy metering: On the property I am renting, the supply voltage is 2 x 110 volts. These 2 x phases enter a energy meter which then exit the meter to over head lines to my house. Question 1. The meter is single phase 240 volts but is being used as 2 x phase(2 x 110volt), is this acceptable? if not, please give me the reasons. The meter details are as follows: 60Hz 15amp Imax 100 amp Kd 3,6 Wh/R 1 fase 3 hilos Model FX 231. I think it was manufactured in Brasil From this meter, the cables run along over head aluminum conductors,I estimate the cross sectional area to be 25mm diameter, but the neutral is only about 10mm square diameter, which cover a distance of 170 meters and then terminate with an underground cable of 65 meter length, total length = 235 meters. There must be a huge voltage drop over this length. This line is protected with 2 x 200 amp aluminum fuses after the meter, there is no main switch in the distribution board. These 2 phases connect directly onto 2 busbars. Surely the neutral should be the same size as the conductors if not more? Question2. What are your thoughts about this installation, should there be better protection, is the neutral too small? During the night, the lights dim then brighten all the time, this cannot be good for my electrical appliances. In my home, I only have a small electric geyser and fridge, my stove works off gas. But when i use other appliances like the washing machine or microwave oven, the light dim. The internal wiring of this house is done with solid hard drawn copper wires and of course, they have to be under rated. I am a retired electrician by trade, but not on the metering and over head mains side, my experience is on the factory maintenance side of things. Your expertise on these matters will be greatly appreciated. Please inform me how to rectify or make any improvements Kind regards, my power bill is very expensive, so I need to know how to bring it lower. Kind regards, Brian
which types of tests are required after commissioning of 6.6 kva tranformer?
How to measure current and voltage in an ELV circuit
Why the resistance grounding (NGR) is better than Solid grounding?
Is there any standard guidelines/Criteria to design NGR/NGT.?
what is the difference between arc and spark
if 1hp jet motar drop voltage when start from 220v to 120v give the reason and solution.
Why is the generator rating always in kVA and motor rating in kW?
What happen if you keep open the Neutral Grounding Switch in open condition of the HT Generator at starting and again on load if it open then?
how to calculate the megger values for motor, cables and transformers?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)