What is the current flow in 230v ac supply ?
What is the current flow in 415v Ac supply ?
Answers were Sorted based on User's Feedback
Answer / naveen
it depends up on the load connected and if same load is
conneted then the current flow in single phase is root
three times more.
Is This Answer Correct ? | 40 Yes | 11 No |
Answer / abhishek0015
It depends upon connected load. As per formula,
P= V*I*(cos phi)-- for 230v supply and
P= sqrt3*V*I*(cosphi)-- for 415v supply
So it means in 230v single phase supply takes almost 3
times more current than 415v three phase supply.
Is This Answer Correct ? | 26 Yes | 4 No |
Answer / arpit
it will be the same since 230volt ac and 415 volt ac are
star connected, in star VL=1.732* vph, and current is same.
Is This Answer Correct ? | 4 Yes | 8 No |
Answer / srujanya,rec
By taking the OHM's Law i.e. V=IR. here we consider R is
constant then V is directly proportional to I. it means If
Voltage increases then current also Increases. in 230V ac
supply gives 23A. In 415V ac 41.5A flows(R=10 ohms)
Is This Answer Correct ? | 18 Yes | 28 No |
Answer / samit sinha
As mentioned by Srujanya, V=IR is wrong it should be I =
V/R because current is proportional to Coltage and not
voltage is proportional to current. When the potential
difference occurs then only current flows - Samit
Is This Answer Correct ? | 3 Yes | 15 No |
what is the meaning of x,m,k in the relays?
why we short ckt the secondry vo5tage/ winding in transfr and motor?
How the circuit breaker is selected for Induction motor of 100 kW, 415 volt, 0.85 power factor, 0.95 efficiency ?
Can i use to 3 phase 4 wire energy meter inplace of 3 phase 3 wire energy meter ?
How the soft starter control the starting current in three phase squirrel cage AC Motor?
what is the difference between the megger and multimeter operation ?
why overload relay is not tripped at time of starting of motor allthough staring current is too high?
can we run the home fan both clock and anticlockwise direction
can any one tell in easy method for circulating current ??
I am an electrical engineer, I found variation in KWH between DG and EB for Same load for same duration, can any one help me why this variation arises?
WHY WE CAN GENERATE POWER IN 3PHASE MODE ONLY NOT IN 4 OR 5PHASE
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.