What is the Difference between E/P Positioner and I/P
positioner in a control valve? In which applications the
respective positioners are used in?
Answers were Sorted based on User's Feedback
Answer / jccarlisle
An I/P transducer is a device which converts a current
signal (usually 4-20mA) to a pneumatic signal (pressure
depends on actuator size requirement). The pneumatic signal
goes either directly to control device (valve, damper, etc)
for operation of the device or to a positioner which
measures the amount of mechanical travel of the control
device and adjusts the input until the exact percentage of
movement called for is achieved.
An E/P is a device that integrates both devices above into
one unit.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / pavan
i think i/p
converter
converts current
in to
pressure,where e/
p converter
converts voltage
to pressure.
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / somaraju
if varing voltage with a constant current it is E/P
if varing current with constant voltage it is I/P
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / mike betts
My understanding that the IP positioner would be that you
are using a current signal (I) and converting it to a
pressure signal (P) in order to operate a positioner valve.
I would call the signal conditioner in this case an I to P
converter.
I am not so sure about EP, but E can be used to mean EMF
which is measured in volts and so could ve voltage to
pressure signal conditioner in the same way as I to P in
the example above.
| Is This Answer Correct ? | 19 Yes | 26 No |
Answer / dennis
The "E/P" elector-pneumatic positioner is used for
operation of pneumatic rotary valve actuators by means of
electroller or control systems with an analog output signal
of "DC4 to 20mA" or split ranges.
I/P not sure yet.
| Is This Answer Correct ? | 2 Yes | 11 No |
Answer / rahul dhumal
E/P is combination of I/P & positioner i.e. the o/p pf E/P is directaly given to the valve actuator.
And in the case of I/p 4-20ma is given to it & output of I/P is given to the positioner .
| Is This Answer Correct ? | 14 Yes | 24 No |
Answer / s.m.patel
I to p means input signal is 4-20MA
E to p means input signal is 0 to 10 VDC
| Is This Answer Correct ? | 7 Yes | 19 No |
what master plc do?
how to calculate range of Dp transmitter
can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).
can you tell me how many stages in steam turbine of 10 MW power plant
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
how to connect transmitter measuring sulfur process? 1-by using long impulse line or 2- by using coated short impulse line
why the derivative in PID is always set to zero?
what is differance between SOE an alarams
What is open loop checking and close loop checking
what is flow equation of kg/hr to m3/hr
Induction type 1-p wattmeter reads ….. a) true value b) apparent value c)volt ampere value
3 Answers Engineers India Limited,
what is stroke check for field instument transmetter's & AOV's
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)