if i change range of flow transmitter in th field then does
it need to change range in dcs?
Answers were Sorted based on User's Feedback
Answer / murali -inst.technologist
if range of transmitter changes in field you have to change
the span of the AI in dcs
other wise
transmitter shows correct reading in field side
but dcs get signal in form of 4-20 ma, then flow reading
shows in DCS is as per old DCS span.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / www.islamqa.com
we have to configure the range in dcs with the new values.
example:
old range:
o - 625 "wc means 4ma at 0, 20 ma at 625
new range:
0 - 2500 "wc means 4 ma at 0, 20 ma at 2500
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 8 Yes | 0 No |
my data card only does run in my mobile so how can change it that it run other mobile & computer and i can stor data in my data card
send me last 5 years questions asked in rrb chennai, for section engineer
can anyone can let me know in Eurotron Micro cal 2+ calibrator in milli amps source mode we are not able to get 20 milli amps output it only produces 1.52 milli amps out, but display shows increase in milli amps , and err6 displays, let me know how to remove the err 6.
difference between plc and dcs?
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
why does a transmitter o/o signal starts from 3-15psi or 4- 20mA?
If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?
8 Answers Bharathi Cement, Titanium,
What is eddy current? Describe the operating principle of proximity probe.
Draw a wheatstone bridge circuit showing supply, meter and 3 wire RTD connection
how to know the URL and LRL for steam drum level and why the calibration range is in negative ?
HOW TO CALCULATE WAKE FREQUENCY FOR THERMOWELL???WITH OUT SOFTWARE..
An engineering term STALL used in compressor operation what it means?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)