How big (size) can the tertiary winding be in transformer?
Can we load the tertiary winding, if yes then how much we
can load it?
Answer / rabramovitz
Tyically for stabilizing an oscillating neutral, about 35%
of the KVA (or VA) supplied. Yes, it can be loaded, as long
as you don't exceed the current rating for its gage (do not
exceed current which causes a temp rise at or below the
class of the transformer). The current capability (if
properly designed)will be about a third of a primary phase
current normalized to the tertiary ratio. (call it NI/3)on
a per phase basis.
Is This Answer Correct ? | 0 Yes | 0 No |
in the exciter the power is feeded from battry or control or whatever.and we need it in the generators for the stating . do we need it in the shutdown also?i mean the exciter>
why generating voltages are of 11kv 33kv 22kv of 11 multiples
working of diesel generator ?
WHAT IS DOL STARTER? HOW IT WORK? GIVE ITS CONTROL AND POWER DIAGRAM .
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
what is difference b/w HT & LT and the range of HT & LT ?
Differentiate between induced emf and self inductance?
How can we convert 11 kv to 440 volt without using transformer ?
How to work definite,over pluxing,revers power,OSR relay
How to checked frequency drive output voltages?
what is power ratio between star & delta connection of 3 phase induction motor
how is classified voltage level in generation,transmission & distribution system?,