WHAT IS THE USAGE OF Buckoltz relay IN POWER TRANSFORMER AND
AND HOW ITS FUNCTIONS?
Answers were Sorted based on User's Feedback
Answer / wasif
in case of fault enormous amout of heat is generated in the
main tank which decompose the oil as a result of which
gases are produced. When the gases travel from main tank to
conservator tank they causes the float of buchholz relay to
be inverted which in result makes the tripping contacts and
thus causes the breaker to be tripped.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nagaraja bagi
Buchholz relay is used for Transformer Internal faults,bcoz
of over load or internal faults more heat will produce it
decomposes the oil and produces the gas and because of
transformer insulation gas will produce and it will try
move from main tank to conservator bcoz it is light in
weight then alarm float will operate and gives the alarm if
it exceeds then tripping float will operate and trip the
Breaker of Transformer.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / anant shetye
In power Transformer Gases form so before putting
Transformer in service we have to release that gases & LET
OIL SHOULD come to conservater tank for safe operation ,if
it is not do so and if you give supply to the transformer
Buckoltz relay gets trip & it provide safety to Transformer.
Is This Answer Correct ? | 2 Yes | 1 No |
1.what is the difference between ct and cvt? 2.what is the difference between pt and cvt? 3.what is the difference between relays and circuit breakers?
For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details.
Why we use a shunt capacitor or synchronizing Motor To Improve a Power factor pls reply me in this mail dinesh_elect_eng@yahoo.com
Caliculate the Specific Fuel consumption of 320 kva diesel genarator set?
What are the types of circuit breakers ?
How to calculate unit consumption on the basis of load. kWH=kwXhrs.is it correct? kw is motor load.What is unit consumption at 100% load, 50% load & on no load.
why there is a temperature rise at different metal to metal contact at cable lug??suppose cable is aluminium and the lug is copper,than why the temperature rise takes place??
can u give me a brief idea about power line carrier communication ??
My energy meter ratio is -/110/root 3,1A and connected line CT is 100/1,PT is 11kv/110 so what is the MF for meter
what will happen if the input of a transformer is dc?
800a siemens vcb in our company can not be closed electrcally an mechanicaly cc and oc coils are found ok. why?