Answer / wasif
in case of fault enormous amout of heat is generated in the
main tank which decompose the oil as a result of which
gases are produced. When the gases travel from main tank to
conservator tank they causes the float of buchholz relay to
be inverted which in result makes the tripping contacts and
thus causes the breaker to be tripped.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nagaraja bagi
Buchholz relay is used for Transformer Internal faults,bcoz
of over load or internal faults more heat will produce it
decomposes the oil and produces the gas and because of
transformer insulation gas will produce and it will try
move from main tank to conservator bcoz it is light in
weight then alarm float will operate and gives the alarm if
it exceeds then tripping float will operate and trip the
Breaker of Transformer.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / anant shetye
In power Transformer Gases form so before putting
Transformer in service we have to release that gases & LET
OIL SHOULD come to conservater tank for safe operation ,if
it is not do so and if you give supply to the transformer
Buckoltz relay gets trip & it provide safety to Transformer.
| Is This Answer Correct ? | 2 Yes | 1 No |
Is HT capacitor rating connected directly to motor terminals , related to motor no load current?
How do we calculate the Out put voltage of generator, after the excitation is being given?
hi....I am from india..i have completed my engineering in electrical and electronics field with 58.4% and my IELTS score is 5.5 bands....Recently i received my I-20 in computer and information science from Troy university in Alabama.On 18th i have a visa interview can u please tell me what type of questions i have to answer ??????
What is the abbreviation of NGT panel
What should be the conservator minimum oil level required in 2 mva transformer
why no load voltage is greater than full load voltage?
High Voltage out door substation-annual maintenance, things to be considered
explain the f=np/120 this equ.how to come 120
3 Answers Jayaswal Neco Industries,
Can someone explain how does an IDMT relay works.
what do you mean by the "bay" in a switchyard? how to determine exact number of bays in a substation?
Instrument connected to a single phase supply
what will happen when the dc supply is given to the capacitor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)