Answer / n. ramesh
Power distribution network is supposed to have a voltage
drop of around 4%. As the utility provider has to assure a
three phase voltage of 415 V at consumer's metering point,
the secondary phase to phase voltage of the distribution
transformer is specifed at 4% higher than standard three
phase-phase to voltage of 415 V, which works out to 433 V.
| Is This Answer Correct ? | 46 Yes | 6 No |
Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work
To compensate Voltage drop at receiving end
| Is This Answer Correct ? | 42 Yes | 12 No |
Answer / ash
433V is the no load voltage. that is when the transformer
is supplied at its HT side but without any load connected
to the LV side.
| Is This Answer Correct ? | 18 Yes | 6 No |
Answer / sagar surve
Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / gopalen sv
When the transformer is installed near to the LV distribution and no significant voltage drop occurs because of short length of cables then the problem of high voltage like 250 volts in single phase results in many fused bulbs. Motors rated at 400 V will experience 430 plus volts. Before deciding secondary voltage such conditions should be taken into account.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / andy d
It is to do with the transformer % impedance, As mentioned open circuit LV side of a transformer would measure 433V, Fully loaded the transformer volt drop is equal to the % impedance. A typical 1MVA DY11 transformer would be around 5% impedance at full load, i.e. the secondary voltage reduces voltage to 411V. This is a lower value then 415V however it is not advisable to run transformers at 100% if you want a long life.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / percy
433 IS LILNE TO LINE VALUE OF 250
415 IS NOT DIVISIBLE BY 1.732
| Is This Answer Correct ? | 3 Yes | 52 No |
How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???
in slip ring motor if motor specification is given how we calculate its rotor resistance in starting
What is the previous name of Cox's Bazar
Can be ammeter and voltmeter used without CT? if not, what is the reason for that?
3 Answers Elektrotek, Toyo Engineering,
Motor and transformer working with same principle so why motor rotates while transformer not?
If R and Y terminals are short circuited,then power will cut. we all know that power cannot be stored.what will happen to already generated power at power station?
Totally how much power will be consumed in 1 hour cotinuous running of electric train engine?
how techometer works and how it will be connected above the flywheel in dg system
WHY WE CAN GENERATE POWER IN 3PHASE MODE ONLY NOT IN 4 OR 5 PHASE?
What is cable gland,why does use for?
what shoud be strength and weakness to impress interviewer????????
What will be happend if we not ground CT secondary?
3 Answers Enercon, Engro, THDC,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)