Answer / n. ramesh

Power distribution network is supposed to have a voltage
drop of around 4%. As the utility provider has to assure a
three phase voltage of 415 V at consumer's metering point,
the secondary phase to phase voltage of the distribution
transformer is specifed at 4% higher than standard three
phase-phase to voltage of 415 V, which works out to 433 V.

Is This Answer Correct ?    46 Yes 6 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / n manivannan

Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work

To compensate Voltage drop at receiving end

Is This Answer Correct ?    42 Yes 12 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / ash

433V is the no load voltage. that is when the transformer
is supplied at its HT side but without any load connected
to the LV side.

Is This Answer Correct ?    17 Yes 6 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / sagar surve

Appliances rated voltage is 415V. If Trasformer is specied
at 415V, it will further drop down at receving end and
appliances may not work

Is This Answer Correct ?    15 Yes 9 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / gopalen sv

When the transformer is installed near to the LV distribution and no significant voltage drop occurs because of short length of cables then the problem of high voltage like 250 volts in single phase results in many fused bulbs. Motors rated at 400 V will experience 430 plus volts. Before deciding secondary voltage such conditions should be taken into account.

Is This Answer Correct ?    3 Yes 2 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / andy d

It is to do with the transformer % impedance, As mentioned open circuit LV side of a transformer would measure 433V, Fully loaded the transformer volt drop is equal to the % impedance. A typical 1MVA DY11 transformer would be around 5% impedance at full load, i.e. the secondary voltage reduces voltage to 411V. This is a lower value then 415V however it is not advisable to run transformers at 100% if you want a long life.

Is This Answer Correct ?    1 Yes 1 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / dheeraj

It is a standard

Is This Answer Correct ?    3 Yes 16 No

Why we Specify Transformer rating 433 V Instead of 415V ?..

Answer / percy

433 IS LILNE TO LINE VALUE OF 250

415 IS NOT DIVISIBLE BY 1.732

Is This Answer Correct ?    3 Yes 52 No

Post New Answer

More Electrical Engineering Interview Questions

Unit of Magnetic Flux Density a) Tesla b) weber c) Hendry d) Farad

3 Answers   Ecil,


What are the disadvantages of autotransformer?

0 Answers  


why do we use star-delta starter. what is its need?

6 Answers  


what are the major difference between 3phase 3wire and 3phase 4wire trivector meter?

2 Answers   L&T, NTPC,


Is there any Flood lighting system which produces more light (More power consumption 1000W,400W etc.,), white light and restart immediately after power restoration ?

1 Answers  






How can we calculate the fault level of the distribution system knowing the percentage impedance of transformer & subsequent equipments.

14 Answers  


How many 2 ton window A/c can runs on a 125 KVA generator?

3 Answers  


sir please send me techinical questions for junior engineer posting in bangalore railway i am diploma holder

0 Answers   RRB,


During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected. Please any body explain that method of insulation is correct or not? also describe of PT connections

1 Answers   Private,


what is JE exam?

0 Answers  


What is the criteria that generally follow by distribution licenses to fix contact demand of their industrial customers?

0 Answers  


when we are going to higher voltage level in substations why we are using Sf6 circuit breakers instead of Vacuum circuit breakers.

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)