One Township having 850 house and each house load is 2.2KW
single phase & 5HP 3 Phase motors of 10 Nos .Who can
calculate 11 KV transformer
capacity .dilip_bhasker@yahoo.co.in
Answer / naresh
The total lighting load of the township is 1870KW and motor
load is 50HP.
We have to load the transformer upto 80percent of
its KVA rating. Because the average power factor has been
taken as 0.8 and to avoid the over loading problem.
So for the township the transformer capacity is as follows.
24x100KVA + 1x63KVA or 15x160KVA + 1x63KVA
Multiple transformers provided instead of few high
capacity transformers to avoid low voltage problem at tail
end.
Is This Answer Correct ? | 2 Yes | 3 No |
WHAT SHOULD BE THE MINIMUM IR VALUE FOR LV (380V) CABLES ACCORDING TO IEC/IEEE.
How does CT can measure the high value DC current?
how to determine the cable size...pls explain me with the formula taking particular load....does the factors like impedance & short circuit rating influence the cable size, if so how....
What is an infinite bus bar?
why do we not use equivalent voltage source in negative sequence equivalent ckt.
how to calculate neutrel current
how to difference between the HT< cables
Explain how you intend to work under pressure to meet up with deadline target?
why transformer rating in kva and motor rating in kw
Why derating factor os applied on Cables?
- two pumps must work with them at the same time but if the first pump start the second pump must delayed for some time to start also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it
why needtwo winding LV and HV in transformer?