a 3 phase slip ring induction motor is wound for 4 poles on
stator and 6 poles on rotor; when 3 phase balanced voltage
source at 50 hz is applied to motor it will run at
a)1500rpm b)1000rpm c)750 rpm d)zero rpm
Answers were Sorted based on User's Feedback
Answer / santosh kawade
If slip rings are shorted it will run at 1500 rpm.
santosh kawade
Is This Answer Correct ? | 24 Yes | 11 No |
Answer / suraj patel
In Indaction motor 120f/p wher consider P is number of pole
for indaction motor this pole cosider only stater coze we
give supply on stater. thus Ans is 1500rpm
Is This Answer Correct ? | 16 Yes | 8 No |
Answer / nagaachi
hey fools
in SIM no:P IN ROTOR = no: poles in staor
what could be the speed i dont know
but i dont answer foolishness
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / mohit
If stator poles and rotor poles are not equal then resultant
torque will be zero and motor will not run.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.sakthi
answer b) 1000 rpm is correct. because 120f/p =N.here N is
the speed of the motor. hence f and p is the input frequency
and no of poles on the stator or rotor respectively
(depending upon which one is the rotating portion of the
motor) so and so, in general rotor is rotating so the answer
b) is correct. if the stator is rotating, answer b) is correct.
thank you....
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / bhautik patel
its bcoz Ns=120f/p
where Ns is the stator sychronous speed
f= supply frequency
p= no of supply poles i.e. stator poles
substituting values f=50 hz , p=4 ,
we obtain Ns=1500 r.p.m
Is This Answer Correct ? | 9 Yes | 4 No |
Answer / angel
how do you know the answer because the number of turn
changed with change in the windings on the coil from the
poles if you only know the freguency it's the same aas not
being given any thing because even the value of the
standard voltage has changed so the answer can not be
determine reason being we don't know the flux windings.
Is This Answer Correct ? | 1 Yes | 0 No |
HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.
Explain the working principle of Synchronous Generator and Assynchronous generator?
Briefing the effects of ASR and ACR of a double closed-loop speed regulating system.
The current though a branch in a linear network is 2A when the input voltage is 10 volts. If the voltage is reduced to 1 volt, and the polarity is reversed, what is the current flowing through the branch ?
How to convert 2 phase to 3 phase electricpower in induction moter?
how did the differential relay work to protect the power transformer
how many types of grounding?
For group 1 , 2 whather i have to prepare my technical or general studies etc? and im graduate in ee engg. for wht posts im eligible for? please tell me!
1.where in India the maximum transmission voltage is operated? 2.what the methods are used to cool down the transformer?give the specific ratings of the transformer & specific cooling process. 3.how zero & negative sequence reactances are formed in a rotating machine when fault occur in the system?
Resistance of low voltage side of transformer compared to high voltage side is A less B equal C more D depens on design
DRAW ACIRCUIT DIAGRAM OF 100 KVA 415V/55-0-55V DELTA TO STAR TRANSFORMER
What is the difference between IS:1554 (Part 1)/1988 & IS:694/1990 ? What do these two standards specify about?