We use ungrounded DC system (220V/110V) for control and
protection system in substations etc. Suppose we have long
2 core DC cables running from our DCDB in control room to
the load (length of around 2 to 3 km). Do we need to
protect these long DC cables from earth leakages or not? If
yes how?
Answers were Sorted based on User's Feedback
Answer / krishna
Usage of differential relay for 220V/110V is not an
economical idea. Differential protection is the costlier
protection. DC Cables should be protected from earthleakage
bacause of which voltage differences occurs and trips the
circuits due to large variations. I suggest to go for
MCCB/MCB of required rating which trips the circuit when
earth leakage occurs.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ch.shankar
use dc differential relay or poles insulation monitor which
will help u to measure leakage
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / k.prakashchandra
Normally dc earth fault locater is employed. If one polarity
shows earth fault there is nothing to panic.Heavy fault
current occurs if the other polarity also develops fault. If
tripping is provided ,the protection may get lost.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sanjay choubey aditya electron
You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sanjay
You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is mimimum di -electric strength value for 33 KV transformer OLTC oil
What are the point of a single core cable to be earthed?
Why Drives are used to run AC motors?
How we can calculate the consumption in kwh of motor on basis of kw @100% load, @50% load & @ no load.
what is the principle of operation of synchronous motor and generator? explain in detail.
What is the function of PMG in DG sets & how it works??????????
can we use NPT glands in LT panel
we have a 2000kva step down transformer at our site. The HT side is charged from 22000V. So the primary current will be 52.48A. So why the HT breaker(SF6 ABB) is rated of 1250Amps ?
What will be the total current for 300kva UPS if it runs on 40 to 45 percent load. Is there any formula for to calculate the exact load.
why DG sets power factor is 0.8 lagging.
Is the theorem applicable to ac sources?
what is induction relay
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)