Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We use ungrounded DC system (220V/110V) for control and
protection system in substations etc. Suppose we have long
2 core DC cables running from our DCDB in control room to
the load (length of around 2 to 3 km). Do we need to
protect these long DC cables from earth leakages or not? If
yes how?

Answers were Sorted based on User's Feedback



We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / krishna

Usage of differential relay for 220V/110V is not an
economical idea. Differential protection is the costlier
protection. DC Cables should be protected from earthleakage
bacause of which voltage differences occurs and trips the
circuits due to large variations. I suggest to go for
MCCB/MCB of required rating which trips the circuit when
earth leakage occurs.

Is This Answer Correct ?    5 Yes 1 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / ch.shankar

use dc differential relay or poles insulation monitor which
will help u to measure leakage

Is This Answer Correct ?    5 Yes 3 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / k.prakashchandra

Normally dc earth fault locater is employed. If one polarity
shows earth fault there is nothing to panic.Heavy fault
current occurs if the other polarity also develops fault. If
tripping is provided ,the protection may get lost.

Is This Answer Correct ?    1 Yes 0 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / sanjay choubey aditya electron

You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.

Is This Answer Correct ?    1 Yes 0 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / sanjay

You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?

1 Answers  


Why the symbol of register is "zig zag"

0 Answers   Suzlon,


How much area is covered by a single lightning arrestor to protect object from lightning strokes ?

1 Answers  


Which Current transformer will be bigger in size, 400/5 or 400/1 & why?

2 Answers   Apollo,


what r the tests on the 3 phase transformers can any one explain how to test using megger on transformers thx

2 Answers  


ceiling fan wattages rating

1 Answers  


why one pin of plug pin is longer than other two? In some mobile chargers one pin is made not conducting .Why?

4 Answers  


Re: can you give main difference between ELCB 2pole And RCCB 2pole? And how this devices operated?

4 Answers  


Why need 3phase machine double earthing?

0 Answers  


how to checking earth restence with earthtester

1 Answers   NTPC,


If I want to use capacitor banks at HT (11 KV) side for maintaining power factor then which type of capacitor should I use? Plz give me the specification?? (I am using 1250 Kva transformer (11 KV/433V)).

2 Answers  


in battery charging room we find two fuses (one in positive other in negative cables ).why it is so?one fuse is ore than sufficient?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)