what r the tests on the 3 phase transformers
can any one explain how to test using megger on transformers
thx
Answers were Sorted based on User's Feedback
Answer / ranjan sannyasi
Many of test over an 3 phase transformer you can done, you
have to mentioned about megger test,so that test what actual
done,it's ur qsn...may i r8?
so, It's actually IR test means Insulation Resistance(IR)
test,how much insulated the transformer winding in between
their winding(primary & secondary).You could be known by
meggar test.
1.1st You have to do the PHASE TO EARTH test,how to do the
test? megger have two terminal,one of them you have to
connect with 1st phase (R-phase) or whatever(it may be
another two Y or B),must be one by one,it ds'nt matter ok,&
another with transformer body,its the earthing path.
regarding this test obtaining three of value must be
100,it's must be noted that 100 value is the accurate,if any
of value is 0 then some where in b/w winding & body it may
be leakage,for that DC current** is flowing through the
winding to earth.
2. 2nd test is the vital one.It's PHASE to PHASE TEST.It's
done by like that, suppose megger one terminal is connect R
phase and another one done by Y phase, so like that 1st R-Y,
2nd Y-B & last B-R, same you have find 3 value,like above
those.If all the value are 100 then its insulation b/w
winding are accurate,there have no insulation fault.
| Is This Answer Correct ? | 6 Yes | 2 No |
With all the connections removed 1.Primary to body 2. Sec to
body 3.Between Pr and Sec .Find PI value also
| Is This Answer Correct ? | 1 Yes | 0 No |
formula for incomer breaker size calculation of powerfactor correction unit
how we control the magnitude of a generator output
How to select transmission line type (i.e. 11kv or 33kv) for new established industries
how to calulate bearing number of any motor ?
What is the different between feeder & bus?
what is the formulae for calculating the cable size for a given voltage and current.
how can we measure the import power and export power in the same line?
why ht line fuse wire is so thin
Why have the transformer one earthing to their neutral? Why have the transformer many earthing to their body?
why the frequency in india is 50 50HZ why we not select the o ther frequncy range?
Explain about 3 phase motor fault current calculation with examples?
Haw to check conductivity of budbar
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)