How will you design a capacitor bank for a plant? if my p.f
is 0.6 i have to improve it to 0.9 or 1 what kind of steps i
have to do? and is there any formula for calculating this?
Answers were Sorted based on User's Feedback
Answer / joel q.
You must add a capacitor bank. you can determine the size
of the capacitor to be added using the following formula.
KVAR = KW*Tan((arccos0.6) -(Arccos0.9))
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / raju
to improve powerfactor only capacitor banks should be used
but not inductor as capacitor having leading pf which wil
reduces reactive power and improves pf
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / kaushik
if we are talking for 0.6 pf laging to 1 pf then we require
a capacitor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
if we are talking for 0.6 pf leading to 1 pf then we require
a inductor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
v=supply line voltage.
i=line current.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amrish sharma
just calculate total load of plant,,, then use capacitor 30
percent rating of total load,,, example if you have hunderd
ampere load then use 30Kvar capacitor,,,
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / saravanakumar
If you want improve your power factor, you should provide a
capacitor bank.The rating of the bank is 1/3 rd of the
transformer ratings.
| Is This Answer Correct ? | 1 Yes | 4 No |
75kw drive operated motor current fluctuation from(85-130)ampere.current setting in drive is 130amp.sometimes motor trip when current limit cross 130amps.I change the drive. still current fluctuate between 80-130amps but in this time motor not trip,current setting in drive is 130amps.where is the problem?
What range of speed can you get with the field control method of speed control of d.c. Shunt motor?
What happens if we give the supply to the rotor of induction motor and make its terminal shorted?
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
in a dc shunt motor what happens if motor takes high current,no speed
AC voltage only create magnetic flux in coils, but in Solenoid coil how 24V DC volt create flux and pick the plunger
What is the possible cause for failure of lightning arrestors in outdoor substation under normal condition
when we supply in primary side of transformer then the supply goes in secondary side?how it works?
I want to know the currect formula for industrial lighting lux caluculation & light fittings selection
Define unilateral circuit?
What is stub protection is all about?
why is it that the HT motors & motors having very low kW rating(<1kW) have windings connected in STAR, whereas the motors having in between kW ratings have DELTA connected windings??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)