How will you design a capacitor bank for a plant? if my p.f
is 0.6 i have to improve it to 0.9 or 1 what kind of steps i
have to do? and is there any formula for calculating this?
Answers were Sorted based on User's Feedback
Answer / joel q.
You must add a capacitor bank. you can determine the size
of the capacitor to be added using the following formula.
KVAR = KW*Tan((arccos0.6) -(Arccos0.9))
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / raju
to improve powerfactor only capacitor banks should be used
but not inductor as capacitor having leading pf which wil
reduces reactive power and improves pf
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / kaushik
if we are talking for 0.6 pf laging to 1 pf then we require
a capacitor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
if we are talking for 0.6 pf leading to 1 pf then we require
a inductor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
v=supply line voltage.
i=line current.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amrish sharma
just calculate total load of plant,,, then use capacitor 30
percent rating of total load,,, example if you have hunderd
ampere load then use 30Kvar capacitor,,,
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / saravanakumar
If you want improve your power factor, you should provide a
capacitor bank.The rating of the bank is 1/3 rd of the
transformer ratings.
Is This Answer Correct ? | 1 Yes | 4 No |
What is meant by unilitrel device?plz tell about h-parametrs
what is AH of battery
why we use battery source for current transformer polarity testing?
Can anyone send details regarding motor protection relays ? their manuals please ?
Define damping ratio.
before transformer oil dielectric strenght tests are taken the oil should be allowed to settle to remove option 1 air bubbles 2 gasses 3 contamination 4 water
what is the working principle of soft-starter & how it diff. from VFD ?????????
what is the distance between two overhead lines
Multimeter show phase to neutral volt 230 the per phase but phase to phase 415 not show 460 why.
what is the disadvantage of lagging power factor & why ?
Why in USA supply voltage parameters(230V,60Hz)are different,is there any advantage please brief.
how to set the transformer differential relay