what is reactive power (MVAR) and how it is control? how it
is generate in powerplant?
Answer / k.prakashchandra
The reactive power on generator can be controlled only if
it is connected to grid/network.If you make the terminal
voltage higher than of grid ,gen will draw inductive power
(lagging pf) and the vice versa.Usually generators are run
at 0.92 to 0.98 lagging pf for system stability.
Is This Answer Correct ? | 19 Yes | 7 No |
What value of resistance required between Saftey earth and instrunment earth , maximum and minimum values required
WHY BREAKER ARE USED IN SUBSTATIONS?
Form fator is the ratio of?
If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rating capacitor used, please give me Calculation. What is effact of consumer & suplier if pf is lagging or leading with on effect machines/ TF/GE etc.
i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?
What is the function of Antipumping Relay and Lockout Relay?
what is real and reactive power?
ELCP USE IN 3 PHASE SUBMERSIBLE PUMP? THEN USE 3 POLE 0R 4 POLE?
What is the difference between Busbar Chambar, MCCB board and MCB Board? How to choose to use which one in the system?
why mostly conductor made by 7 nos wire?
Sparking occur when a load is switched off because the circuit has high – a.) Inductance b.) Capacitance c.) Resistance d.) None
How to check 11000/1.732 to 110/1.732 Potentila transformer (PT)?