why not use capacitor in Dg sets.
Answers were Sorted based on User's Feedback
Answer / raj
No, we can add capacitor till pf=0.95 it will reduce the
line current so the losses and heating but it should not go
to leading side and if dg set running in parallel then pf
should be kept 0.9 so that stability and load sharing
should be proper.even i have used capacitors in dg so many
times successfully without trouble.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / meeran
the DG Designed constant power factor .8 no need capacitor
output load always constant if we add capacitor it will we
additional load and it will not use for power factor
improvement.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sonu
No, we can add capacitor till pf=0.95 it will reduce the
line current so the losses and heating but it should not go
to leading side and if dg set running in parallel then pf
should be kept 0.9 so that stability and load sharing
should be proper.even i have used capacitors in dg so many
times successfully without trouble.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / parminder singh
The generator for d.g set is designed at 0.8 power factor.
our load is always between 0.8 - 1.0 p.f. so if we connect
capacitor it will overload the dg set.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / ajit
capacitor is not use in dg sets because in dg sets power
factor already disign by manufacturer acording to your
requarment or type of electrical load.mostely dg sets
desion on .8 powr factor
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / preetha
DG produces DC only which is being resisted by Capacitor
| Is This Answer Correct ? | 1 Yes | 10 No |
why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)
Difference between rating factor of cable and derating factor of cable?
200-100/1-1A – Transformer Knee point voltage
My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?
Why most of analog o/p devices having o/p range 4 to 20 mA and not 0 to 20 mA ?
11 kv metering is done in my factory.Meter show PF 1.000 but kvarh lag&lead show 24&94 respectively & Avg.PF is .956 .? is what i do for inproove my PF to 1.000
What are the different protection systems takes place on control panel board?
My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there any possibility of Technical Problem ?
the problem faced on star or delta winding connection??
pls tel me the electric train traction motors name plate details like rpm,torue,voltage,amps,watts..ect..
Do you know how to connect a motor of different H.Ps?
what is The difference between national electrical code and I.S.Code (electrical) and what is the value of NEC in electrical engineering field
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)