Answer / vinoth
Earth Connected to Neutral on Transformer Installation, Beacuse if Suppose fault current apper in circuit that time the current want to ground,If No Earth For Neutal Means it will affect the transformer windings only.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / pradeep
In fact, transformer neutral is grounded for a star connected winding.
there are several reasons for neutral grounding in a transformer.
1. the main reason is to avoid automatic neutral shifting problem due to unbalanced loading.
2. Neutral can also be grounded to introduce the protections related to earth faults. So that the internal/external earth faults can be identified in the first instant in order to isolate the faulty circuit as faster as we can.
3. Neutral grounding can also be done through a series resistor/reactor or a transformer to limit the fault below certain level and to avoid the problem of "Arcing grounds"
4. Personal safety
5. Reduced magnitude of transient over voltages
And so on...!!
Is This Answer Correct ? | 1 Yes | 0 No |
what is the importance of earthing system on the generators big capacity and small?
Why thwe Direction of Rotation of a TABLE Fan & CEILING Fan are different?
what is transformer tap change HT side and LT side
what instruments used for measuring of inductance and capacitance.
In generation,transmission and distribution voltage frequency is either 50HZ or 60 HZ;why are only these frequencies?
What happens to voltage when current through the inductor is constant?
how to commissioning the genset with amf panel?
what is electrical?
My energy meter ratio is -/110/root 3,1A and connected line CT is 100/1,PT is 11kv/110 so what is the MF for meter
induction motor. we have a three phase supply from diffrent source like R= transformer. Y = DG sets. B = ups. if motor is runing.
Give the selection criteria of a 3 Phase transformer for industrial purposes ?
will 1050kva DG set withstand for back charge of 16MVA transformer