Why TAP changer provided in primary side of HT
transformer ? and why not in secondary?
Answers were Sorted based on User's Feedback
Answer / yash
1. at HT side current value is less as compared to LT side.
2. insulatin requirement is less
3. tap changing can be smoother and it would have fine
control as no. of taps are more(due to low current)
Is This Answer Correct ? | 76 Yes | 3 No |
Answer / k. tivaganon
In theory, tap changer can be in any side of the
Transformer. Normally, for a step-down Tr., we put the tap
changer on the High Tension side due to many number of
turns of winding, in which we can tap easily. On the
contrary, if we put the tap changer on the Low Tension
side, there is not much turn of winding to use!!! For the
Distribution Tr., normally the tap changer will be NVTC- No
voltage tap changer. That is, no voltage no current go
through the tap during the change of tap position (There
will be no spark!!!!) For larger Power Tr., OLTC- On-Load
tap changer will be used. Tap will change position under
energized power.
Is This Answer Correct ? | 44 Yes | 3 No |
Answer / sanjay yadav
due to low current in HT side , Secondary side flow High
Current
Is This Answer Correct ? | 51 Yes | 17 No |
Because of High Voltage in primary side, it will draw less
current. While changing the tap, Due to less current
sparking occurs less.
In secoondary side low voltage, so high current in
secondary, and more sparks due to high current.
Sundaramahalingam_a@yahoo.in
Is This Answer Correct ? | 31 Yes | 3 No |
Answer / k1
There are two reasons; one reason from electrical and the
second one from practical point of view:
1- Low current on HV side makes tap changing smoother and
lowers stresses on the diverter switch.
2- HV windings are generally on the LV windings(consider
concentric HV and LV windings). Therefore the wiring of the
taps would be easier in comparison to the case where the
taps on LV side may be wired through HV windings.
Is This Answer Correct ? | 7 Yes | 6 No |
Answer / naaz
Because of in HT side voltage is large and current are less and chances of sparking are less that's why we provide tap changer in primary side
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jayakumar
If only one tap changer is required, tap points are usually made on the high voltage, or low current, side of the winding to minimize the current handling requirements of the contacts. However, a transformer may include a tap changer on each winding if there are advantages to do so. For example, in power distribution networks, a large step-down transformer may have an off-load tap changer on the primary winding and an on-load tap changer on the secondary winding.
Reference from Wikipedia
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / ram sumer
This depends on your use,for which perpose transformer is
been used. If the transformer is usde for long distance
transmission line i mean in delta to delta HT transformer
tap changer will be provided on primary side. To cover the
line losses which make a cause of voltage drop,when primary
side tap is changed in ratio of that tap position secondary
will also increase or decrease the voltage as you desire.If
you provide it on secondary side it will oppose the primary
voltage
But in case of distibution transformer i mean delta to star
tap changer is provided at secondary side.
Is This Answer Correct ? | 4 Yes | 14 No |
if you provide tap changer on ht side we variy the voltage
as we required at secondary side if we connect in secondary
side we can variy the current as the changes in load
Is This Answer Correct ? | 10 Yes | 31 No |
Technical requirement of Copper earthing over GI earthing.
what precautions to be taken while desigining a LT,HT panel. Eg-LT panel PCC panel with ACB installed. HT panel VCB panel with VCB installed. & what is main diffrence betwn IP54 & IP55 construction of panel.
A 3 phase transformer's (Y-Y) Y and B phase is (Y and B connection not broken) broken from neutral and R and Nutral connection is ok, what will be the relay tripping and why
comparision between mcb,mccb,elcb,flcb,elcb in details
What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?
what will happen if OLR CT in all phases are short circuted
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. Between alternator & breaker one stepup transformer used. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
Basic laws governing motor and generator
what is meant by rotating magnetic filed
hello everybody...i m an Elelctrical Engineering student.. i m in final year.. i m attending IOCL interview on 2nd aug. kindly let me know on wat subjects to concentrate more...any body who has attended the interview can help... others can also post their views... thankyou.
Define ampere
Can any body tell me the different types of LT cables & their application.