HOW TO CALCULATE THE SIZE OF CABLE COPPER & ALUMINIUM
Answers were Sorted based on User's Feedback
Answer / kalirajan.n
TAKE A LOOK IN THE FORMULA BELOW....
VD= 2*K*I*L/ CSA
WHERE:
VD= VOLTAGE DROP
I= CURRENT
L= DISTANCE OF THE LOAD FROM THE OUTLET (IN FT)
K= 12 FOR COPPER AND 19 ALUMINUM (FOR MAXIMUM TEMP OF 75 DC)
CSA= CONDUCTOR CROSS SECTIONAL AREA IN CIRCULAR MILS.
| Is This Answer Correct ? | 55 Yes | 20 No |
Answer / himadri nayak
Copper Wire
Single Phase/Circuit
Voltage 240
Power(W) 1000
Power Factor 0.8
Resistivity(at 15 c) 1.72E-08
Tempertature 35 C
Resistivity 3.096E-08(for copper)
Length(m) 300(phase+neutral)
Cross section(m2) 0.000006
Resistance 1.55
Load 5.21
Voltage drop 8.06
Percentage 3.36(Do not go above 3 %)
Actual voltage 236.64
Actual Current 5.28
This is a sample of how to calculate wire size for single phase copper wire. If you want contact me for the excel sheet for copper/Al, 3phase/1 phase calculation.
@ himadrinayak@yahoo.co.in
| Is This Answer Correct ? | 31 Yes | 5 No |
Answer / dilawar husain
yes,these factors are important for cable sizes.
| Is This Answer Correct ? | 25 Yes | 7 No |
Answer / venkat iyer
Factors that to be considered are;
1. ambient temperature
2. permitted temperature rise
3. factors applicable due to method of cable laying
4. factors applicable for group running of cables
5. spacing between cables
6. permitted voltage drop say 2.5%
| Is This Answer Correct ? | 24 Yes | 7 No |
Answer / jignesh panwala
IT IS BAISICALLY DPEND UPON THE LOAD.
SUPPOSE 53 A LOAD.
53/1.5= 35 HP
35*0.746=26 KW
26000/690=38 SqMM
THIS CALCULATION IS FOR AL CABLE
| Is This Answer Correct ? | 34 Yes | 20 No |
Answer / sivakumar
As per answer no 5, how you take 1.5 and 690 values for
calculation? is there any reference about that value
| Is This Answer Correct ? | 22 Yes | 8 No |
Answer / rajnikant
Dear himadri,
i need more details for the calculation of copper and
aluminium sizes of cable and current capacity.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / bubbly
Actually all brothers we want to know calculation of cable
not VD so please any one have calculation of cable on load
& distance attach here
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / kalirajan.n
***SUPPOSE WE USE COPPER CONDUCTOR AND WE ALLOW A MAXIMUM OF
5V MAX. VOLTAGE DROP:
5= 2*12*15*230/CSA
CSA= 82800/5
CSA= 16560 CM
FROM COMMERCIAL REFERRENCES:
15560 CM IS CLOSEST TO 16510 CM WHICH IS #8 COPPER OR 8 SQMM
WIRE.
NOTE:
1. IN THIS CASE A MAXIMUM OF 5 VOLTS WAS CONSIDERED IN THE
CALCULATION.
2. THIS CALCULATION IS NOT VALID FOR LARGE MOTORS. BECAUSE
MOTORS DRAWS A MAXIMUM OF 7OO% TIMES ITS FULL LOAD TORQUE
DEPENDING ON THE MOTOR CONTROL STARTING METHODS USED BY THE
DESIGNING ENGINEER.
| Is This Answer Correct ? | 14 Yes | 8 No |
Answer / rohit
Dear himadri nayak could you please tell me the formula to
calculate V.D...and exact formula for calculation of cable
size..but not taking any factor as assuming,,,and if u r
assuming then hw ur assuming????dear you can mail it to me
if you dont mind..
Thanks & regards
ROHIT
waiting for your reply ASAP....
| Is This Answer Correct ? | 5 Yes | 2 No |
Is there any difference between circuit breakers and isolators
Hello everyone, somebody knows what is a "surplice power" ? The hole phrase is: "This rating is appropriate for a generator set paralleled with an infinite bus e.g. a national electrical supply network or grid where the generator set is run at 100% load, 24 hours a day, 365 days a year and any surplice power is exported into the grid" Thanks in advance.
why we are using the ac supply in domestic purpose, why don't use dc supply.
Is a d.c.compound motor is use as a booster? how?
how much percentage set in transformer diffrencialrelay
what is diffrential relay used in generator plz give brief explanation
how can we change the supply voltage?
why steady state stability limit is greater than transient stability limit ? How it can be explained ?
What is star-delta transformer?
From an electrical motor & electrical generator, which has more efficiency & why?
hi friends iam collecting details about motor,generator & transformer so send some web links to about motor,generator & transformer ,please help me .i need your help.thank u
Why induction motor can not be operated at synchronous speed?? what would happen if it is operated at synchronous speed??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)