2 hp motar how many amps taken please show me the formula
Answers were Sorted based on User's Feedback
Answer / gaurang bhavsar- jr. asst. ele
Elect. Power(3-ph)=1.732*V*I*p.f.Now,
2h.p.=2*0.746=1.492=1.5 kw. So, If a voltage system of 3-
ph,415V, 50 Hz is taken, assuming a p.f. of 0.8 then--
1.5=1.732*0.415*I*0.8 which gives I=2.6085 Amp of normal
current. The starting current will be approx. 3 times of
normal current i.e.-7.82 Amp.
Is This Answer Correct ? | 20 Yes | 3 No |
Answer / kanchan mukherjee
p=1.732*v*i*.8
p=2hp=1.5kw
v=415
1.5*1000=1.732*415*i*.8
i=1500/1.732*415*.8
i=2.7 amp.
Is This Answer Correct ? | 3 Yes | 0 No |
What is minimum phase system?
We have studied about many techniques for finding the stability of system, ROOT LOCUS, ROUTH, BODE PLOT, POLER PLOT etc. In these which is used where. what are the difference among them... PLZ tell me.......
what should be distance between two electrical earthing pit as per i.e.e
Can anyone explain how the vector diagram of a transformer which doesn't have name plate be found whether it is Dy11/Dy5/Yd11 and so on?
how to make parrallal ups
how to calculate the breaking capacity of different breakers.
what is working parincipal of a ht transformer
how many units will 100 kvar capacitor consume for one day?
what is RFCT and Insulgard Relay & It's function?
how to Select its CORE in electrical cables based on its applications? or Application of various types of electrical cable based on it CORE?
DEAR SIR, HOW TO CALCULATE WELDING TRANSFORMER CAPACITY IN KW OR KVA (POWER). TWO WELDING TRANSFORMER USED WHAT TYPE OF DG SET CAPACITY LIKE ( 45 KVA OR 62.5 KVA), PLEASE TELL THE WELDING TRANSFORMER RATEINGS. I AM REFINARY (TANKS WELDING) THANKING YOU
what is 3 phase motors