2 hp motar how many amps taken please show me the formula
Answer Posted / gaurang bhavsar- jr. asst. ele
Elect. Power(3-ph)=1.732*V*I*p.f.Now,
2h.p.=2*0.746=1.492=1.5 kw. So, If a voltage system of 3-
ph,415V, 50 Hz is taken, assuming a p.f. of 0.8 then--
1.5=1.732*0.415*I*0.8 which gives I=2.6085 Amp of normal
current. The starting current will be approx. 3 times of
normal current i.e.-7.82 Amp.
| Is This Answer Correct ? | 20 Yes | 3 No |
Post New Answer View All Answers
While performing stability test of differintial cts how to know the voltage and current on both side of the transformer?
how we decide scurt (disc) of insulator with respect to kv rating
What is rotating magnetic field?Discuss elaborately.
Is a direct shorth ciruit on a branch MCCB in a Low Voltage Switchboard a correct means of tesing the performance for discrimination?
Why does inductive loads consume KVARs?
how we provide neutral earth on synchronising panel as per electrical standards?
how to calculate fault level?
What is the suitable transmission voltage?
What is the ratio of Booster transformer?
Whats the minimum value for I.R. that can be allowed for HT & LT alternators for operation?
what is the question paper model for section engineer in RRB
gas turbine genrator reactances
What is DTR erection?
i need the details about bhel exam.how to apply for that.please send to my email-id.thenmozhi2k7@gmail.com
difference between main metering kiosk and check metering kiosk