2 hp motar how many amps taken please show me the formula
Answer Posted / kanchan mukherjee
p=1.732*v*i*.8
p=2hp=1.5kw
v=415
1.5*1000=1.732*415*i*.8
i=1500/1.732*415*.8
i=2.7 amp.
Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
how to calulate short circuit current for the following: 1.cable connecting 11KV of 22KV/11KV transformer to 11Kv of 11KV/415V transformer 2.what cable size should i use.
What is the difference between acs 550 & acs 850
Explain the operation carried out in thermal power stations?
The gauge indicates the number of amps, but what about voltage? How voltage rating (for wire or fuse) determined?
what is the voltage between earth to neutral in lift.
what is servo motor & how does it work.
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?
how to calculate the loss tangent of electrical cables
how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?
What are the functions of temperature scanner in power transformer?
What Is Connection APFC Panel In Compony.
Why in power plant projects we see DOL starting method used for motors upto 160 kW instead of star delta method
STATE WORKING OF VACCUM CIRCUIT BRAKER?