2 hp motar how many amps taken please show me the formula

Answer Posted / kanchan mukherjee

p=1.732*v*i*.8
p=2hp=1.5kw
v=415
1.5*1000=1.732*415*i*.8
i=1500/1.732*415*.8
i=2.7 amp.

Is This Answer Correct ?    3 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how to calulate short circuit current for the following: 1.cable connecting 11KV of 22KV/11KV transformer to 11Kv of 11KV/415V transformer 2.what cable size should i use.

1737


What is the difference between acs 550 & acs 850

5468


Explain the operation carried out in thermal power stations?

700


The gauge indicates the number of amps, but what about voltage? How voltage rating (for wire or fuse) determined?

1631


what is the voltage between earth to neutral in lift.

1443






what is servo motor & how does it work.

1607


if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.

1671


stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate

2329


Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?

1139


how to calculate the loss tangent of electrical cables

1724


how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?

2599


What are the functions of temperature scanner in power transformer?

1715


What Is Connection APFC Panel In Compony.

1026


Why in power plant projects we see DOL starting method used for motors upto 160 kW instead of star delta method

1479


STATE WORKING OF VACCUM CIRCUIT BRAKER?

1558