in thermal overload relay class 10A indicate what
Answers were Sorted based on User's Feedback
Answer / paul
I am not aware of Class 10A, I am aware of Class 5, 10, 15,
20, 25 & 30. These refer to the tripping curve of a
thermal/electronic relay - eg Class 10 means 6 x motor full
load current (FLC) for 10 seconds (normal squirrel cage
induction motor). Therefore Class 30 means 6 x FLC for 30
seconds and Class 5 means 6 x FLC for 5 seconds etc....
Is This Answer Correct ? | 19 Yes | 1 No |
Answer / amit
10 A means tripping class of relay..like10,20,30 A
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / jayant jain
Class 10A relays are those that will trip within 2 to 10
seconds when supplied with 7.2 times the current setting.
Similarly there are Class 10, 20 & 30 relays where the
tripping times at 7.2 times the current varies. The class is
helpful in correct selection of the relay for your motor
protection as it takes into account the heavy start or
normal start of your motor.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jitendra gosai
Standard tripping classes are 10 A, 10, 20, 30. The
tripping
class indicates according to IEC 60947-4-1 the maximum
tripping time in seconds under specified conditions of test
at
7.2 times the setting current and specifics tripping and non
tripping times for 1.5 and 7.2 times the setting current.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jothiswaran.s
Adding to Mr Paul , the class of relay indicated the error
percent. usually matched with the CT. also they will not be
marked as "class 10A"
Is This Answer Correct ? | 0 Yes | 3 No |
what is the diffrence between resistive load and capoasitive load.?
if 300 hrs not comleted at wat interval b.c,d checks og take place
Why dose an electric meter record KVA when there is no load on a 500 KVA transformer
What is the name of the winding to which supply is given?
working
how to choose cable size with respect to load? how to convert cable size in mm2 to sq.mm?
Can I do body earthing of machine by using Cable armour or I have to run another GI wire for body earthing and how many wires I need to run. Is there any rule for this. eartnig
why do we require two lines one phase and a neutral for an ac transmission..is neutral potential zero..?if yes y carry a neutral line from generating station itself...why dont we take it from ground
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
how to calculate the bus-bar size. give formula with description
what is the procedure for erection of a transformer
how does it help for selection of a transformer.