is there or does RCCB work for single phase connection?
Answers were Sorted based on User's Feedback
Answer / samir
RCCB is nothing but only a current transformer which
detects the difference of incoming and outgoing
current,while in phase wire draws 1 amp and 1 amp returns
in neutral the net current of of CT secondary will nil,but
when Phase wire draws 1 amp and neutral will return 900 ma
(in case of leackage due to bad insulation of equipment) so
net difference of 100ma will be detected by the CT and its
secondary connected with coil and plunger,plunger will
actuate and it will trip RCCB mechanically.
Is This Answer Correct ? | 8 Yes | 0 No |
How do you compute voltage drop and cable size over distance?
how much earthings are provided for 22KV HT Metering Kiosk
1 Answers GE, Gionee, Knight Frank, TATA, Vacmet,
why we did not get shock by touching +ve OR -ve busbar (Which are going to supply cell voltage) of Rectifier- Tranformer in electrolysis plant?
sir, What is the purpose in Generating power plant is operated Lagging PF and Above 0.9 lag PF?
What are gain margin and phase margin?
In VSD (variable speed drive)I/P and O/P connections given wrongly what will happen?
What must the distance between two MV cables be when they are laid on tray?
What will happen if we parallel two transformer with different %impedace?
any one can explain the stages of a knee point which is taken during ct magnetising curve.
what is the difference between droop mode and ischnorous mode in thermal powerplant?
does buccholz in a transformer use batteries
What should be value of Circuit breaker operating time and tripping time?