Answer / samir
RCCB is nothing but only a current transformer which
detects the difference of incoming and outgoing
current,while in phase wire draws 1 amp and 1 amp returns
in neutral the net current of of CT secondary will nil,but
when Phase wire draws 1 amp and neutral will return 900 ma
(in case of leackage due to bad insulation of equipment) so
net difference of 100ma will be detected by the CT and its
secondary connected with coil and plunger,plunger will
actuate and it will trip RCCB mechanically.
Is This Answer Correct ? | 8 Yes | 0 No |
HAI,HOW TO SET THERMAL OVERLOAD RELAY FOR DOL STATRTER FEEDER AT START AND RUNNING?
how power can be saved using VFDs in detail explain
I have cleared IOCL written exam(Electrical). My intv is on 6/9/2008.can anyone guide me & tellme abt intv questions.
what are 3 factors when selecting a contactor for a job?
The MCB circuit breaker have a voltage rating of 440VAC it's possible to supply a voltage of 480Vac
What is the equivalent circuit of a transformer and its vector diagram?
how i prepare for the written test in mahagenco?
2 Answers MahaDiscom, MahaGenco, Wipro,
Explain UPS
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
In India the supply voltage is 230 volt A.C. During the negative half cycle phase becomes neutral and neutral become phase? or what will happen during negative half cycle? how the electrons flow during positive and negative half cycle?
what is meant by carrier aided trip protection in transmission line
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??