What is the Different between CT Class-0.2 & Class-0.2s ?
Answers were Sorted based on User's Feedback
Answer / sam
Accuracy class of 0.2 means +/- 0.2 % error. But, the
declared accuracy is guaranteed only between 100% & 120%
rating. And, with some increased error, the CT performance
can be guaranteed from 5% loading. Below this load, the
error is not guaranteed. It can be anything.
Normally these classes of accuracy are used for Tariff
Metering by the Utility Company.
In large industrial projects, the project would be
commissioned in steps only. In such a case, initially the
loading will be very low. If the tariff metering CT errors
are haphazard, it may not be acceptable either to the
supplier (in case of negative error) or to the consumer (in
the case of positive error). And the magnitude can be quite
large, say, with a sanctioned demand of 10MVA, even 1%
error means 100kVA.
To cater to such situations, Standards have introduced two
new accuracy classes, 0.2S & 0.5S for tariff metering
purposes. These special CTs guarantee the declared
accuracy, even with 20% loading. And some definite error
can be defined even with a load as low as 1%. Thus they are
suitable for industries where loads are commissioned in
steps or stages.
Is This Answer Correct ? | 44 Yes | 5 No |
Answer / k.prakashchandra
's' stands for special.0.2s class cts guarantee the the
specified accuracy even at 1% and 120% of rating where 0.2
class cts may not be accurate upto 5% and beyond 100% 0f
rating
Is This Answer Correct ? | 27 Yes | 4 No |
Answer / rao
For 0.2 Class specified accuracy is 'defined' between 5% to 120% of rated current, whereas for 0.2 S the accuracy is provided between 1% to 120% of rated current. At these secondary current ranges, accuracy is applicable when the burden is between 25% to 100%.
Is This Answer Correct ? | 1 Yes | 1 No |
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
how can H.V busbar in a powerstation can be protected?
what is practical efficiency of power transformer..?
what is the difference between the alternator used in hydro and thermal power plants??
What are the uses of MCB & ELCB ?
checklist of ELCB
How we can determine short circuiting current any plant and for example a plant which power generation is 415 volts and plant load is 500 kw.
We have two APFC panels in same station. I need how to connect CT in two APFC panels.can we take one CT in series connection or two separate CTs.
how to test an MCB
what is range ACB
At full load wat is the motor p.f And at no load will is the motor p.f?
how can we change the phase angle b/w two phase?