Answer / vishvesh
yes, we can connect this three generators in one busbar,
after fulflling following conditions.
1.voltage should be same.
2.frequency should be same.
3.phase sequence should be same.
after shynchronizing of all three outputs, we can
connect it to the common busbas.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / guest
we have to synchronise 3 dg for busbar connection.basic
conditions r
1.freq of all dg should be same.
2.phase seq shold be same.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / milinda4p
to connect 2 or more generators to a common bus those
generators should be synchronised.it means
1. frequency should be same (every generator should operate
in same frequency)
2.voltage magnitudes should be same at each bus (i:e if the
generators have different rated voltage outputs correct
transformers should be used to get the same voltages at the bus)
but the POWER RATING is not going to cause any problem for
synchronizing
But in supplying a load after connecting it is important to
adjust the power supplied according to the load.( should
maintain the frequency of the system in constant value. if
not the rotor speeds of the generators should go up or down
causing and destruction or stopping of generators )
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / n rajesh
No,because the following points should be taken,
1.Phase sequence should be same.
2.voltages should be the same.
3.Frequency should be same.
4.Power rating should be same.
| Is This Answer Correct ? | 0 Yes | 3 No |
what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?
what is difference bwt active&passive component
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
i m electrical diploma holder i want to do plc $ Scada some body tell me which insitute is best for me near chandigarh
Why temperature rise test is conducted in bus bars and Isolators?
why the supply power frequency is 50hz in india? where as it is 60hz in US?
what is the speed of the darkness?
What is the suitable rating of MCB for 1.5 Ton A.C and why? 1Ton= how many amperes?
why do we have spikes enough to burn electronic boards, when generators are not grounded
why the name mho relay,despite the locus of circle is impedance?
WHAT IS THE NECESSITY OF GIVING PARTICULAR COLOURS FOR 3 PHASE TRANSFORMERS.....
For these 2 devices what their power ratings are ? 1) single phase : AC 220V & starting amps 3Amps (i.e. starting torque) and the stabilized amps 2A ... For deep freezer 2) single phase : AC 220V & starting amps 2.7Amps (i.e. including the starting torque of a CRT monitor) and the stabilized amps 1 Amps thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)