We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we
connect in common busbar&we have variable load.
Answers were Sorted based on User's Feedback
Answer / vishvesh
yes, we can connect this three generators in one busbar,
after fulflling following conditions.
1.voltage should be same.
2.frequency should be same.
3.phase sequence should be same.
after shynchronizing of all three outputs, we can
connect it to the common busbas.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / guest
we have to synchronise 3 dg for busbar connection.basic
conditions r
1.freq of all dg should be same.
2.phase seq shold be same.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / milinda4p
to connect 2 or more generators to a common bus those
generators should be synchronised.it means
1. frequency should be same (every generator should operate
in same frequency)
2.voltage magnitudes should be same at each bus (i:e if the
generators have different rated voltage outputs correct
transformers should be used to get the same voltages at the bus)
but the POWER RATING is not going to cause any problem for
synchronizing
But in supplying a load after connecting it is important to
adjust the power supplied according to the load.( should
maintain the frequency of the system in constant value. if
not the rotor speeds of the generators should go up or down
causing and destruction or stopping of generators )
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / n rajesh
No,because the following points should be taken,
1.Phase sequence should be same.
2.voltages should be the same.
3.Frequency should be same.
4.Power rating should be same.
| Is This Answer Correct ? | 0 Yes | 3 No |
Shall I use 40A semiconductor Fuses in 32 A SFU ? Frame size is same. What Happen if Fuses burn on SFU?
Explain the terms real power, apparent power and reactive power for ac circuits and also the units used.
what is the HT motor current setting (Motor protection relay)aganist FLA If the capacitor is connected in parallal to the motor to increase the P.F from 0.89 to 0.99. the setting is to be reduced. what is the formula for to calculate the current.(FLA - CALCULATED CURRENT!= )
how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on star-delta starter?
For which purpose the temp. rise test of transformer is conducted?
why does in transformer the v/f ratio constant?
Define the term Capacitance and Inductance?
Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue
Why an ac systems are preferred over dc systems?
what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?
0 Answers Apotex, Periyar Chemicals,
why double earthing is required for welding machine & electrical tools.
Why are tertiary windings used in transformers?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)