We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we
connect in common busbar&we have variable load.
Answers were Sorted based on User's Feedback
Answer / vishvesh
yes, we can connect this three generators in one busbar,
after fulflling following conditions.
1.voltage should be same.
2.frequency should be same.
3.phase sequence should be same.
after shynchronizing of all three outputs, we can
connect it to the common busbas.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / guest
we have to synchronise 3 dg for busbar connection.basic
conditions r
1.freq of all dg should be same.
2.phase seq shold be same.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / milinda4p
to connect 2 or more generators to a common bus those
generators should be synchronised.it means
1. frequency should be same (every generator should operate
in same frequency)
2.voltage magnitudes should be same at each bus (i:e if the
generators have different rated voltage outputs correct
transformers should be used to get the same voltages at the bus)
but the POWER RATING is not going to cause any problem for
synchronizing
But in supplying a load after connecting it is important to
adjust the power supplied according to the load.( should
maintain the frequency of the system in constant value. if
not the rotor speeds of the generators should go up or down
causing and destruction or stopping of generators )
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / n rajesh
No,because the following points should be taken,
1.Phase sequence should be same.
2.voltages should be the same.
3.Frequency should be same.
4.Power rating should be same.
Is This Answer Correct ? | 0 Yes | 3 No |
What is the role of the 50 STUB protection at a GIS 400KV substation with SIEMENS protection relays?
in 31.5 mva power transformer how to set of wti and oti?
what is use of governer in diesle engine
Difference between single phase and three phase?
why motor run slow speed in star connection?explain how?
What is a thermocouple, and it working principle?
what is function of INVERTER
On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?
0 Answers TNEB Tamil Nadu Electricity Board,
Plz tell me how we can find that particular company has vacancy or not
To prove the capacity of a 10MVA transforemr with 6.5% impedance by a short circuit test how much power is needed to inject an impedance voltage if we have to arrive for its rated current?
Why the bypass and blocking diodes are used in solar modules?
why motor starting current is High ?