Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to find motor contactor rating and bimetalic relay
rating? of 30kw motor which will operate on star-delta
starter?

Answers were Sorted based on User's Feedback



how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / elangovan t

You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span

Is This Answer Correct ?    17 Yes 2 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / ashish

FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).

Is This Answer Correct ?    4 Yes 4 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / aksx

how to find relay range and relay setting of three phase induction motor of 30kw ratting.

Is This Answer Correct ?    0 Yes 0 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / thakur

Full Load Current of Motor-52Ampas per(415.1.732.0.8)

Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)

Is This Answer Correct ?    10 Yes 13 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / abhijit

as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling

Is This Answer Correct ?    1 Yes 4 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / sanjay

40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.

Is This Answer Correct ?    9 Yes 26 No

Post New Answer

More Electrical Engineering Interview Questions

What happens if we connect a single phase energy meter in reverse polarity.

0 Answers  


Dear Brother can u tell the proper size selection of cable & the fault level calculation of braker, busbar etc. pls mail me at azeemk30@gmail.com

0 Answers  


How to synchoronize the generator (with gcb,GT) to grid????? ????? from Grid iam getting power (rated 400kv/20kv) through GT and its goes to UAT.,,ST.,, now my generator(rated 20kv ) ready.,, now iam closing my GCB.,, in GT iam suddenly giving 20kv on that Gt.,, what will happend

0 Answers  


how can we generate electricity????

6 Answers   Torrent Power,


what is the maximum Load capasity in LV-Panel,MDB,SMDB & Final DB'S in Electrical disribution system?

2 Answers   Sterling,


how 650 volts creates? where is use?

0 Answers   DCL,


Is it posssible to obtain the higher speed(3000rpm) for adiferentiallly cascaded induction motors(with 8 and 6 poles)

3 Answers  


it is clear that volts equal to the current as per ohms law. is it appliable to the AC power or only for DC. if it is appliacable to AC in transformers when voltage increases the voltage decreases ????? why??????????????

13 Answers   Bhel,


What are the application of Under voltage release?

2 Answers   Techno Electric and Engineering,


please send privious years question papers of jindal steel and power ltd.My e mail id is rajanikant.sngh@gmail.com

0 Answers   Jindal,


What will be the minimum megger value of 1700 KVA Transformer? a) Do megger value varies according to climate conditions and area . b) If megger value is 100 mega ohm is it good for new transfomer. Explain?

4 Answers  


In which iron losses is higher induction motor /transformer

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)