how to find motor contactor rating and bimetalic relay
rating? of 30kw motor which will operate on star-delta
starter?
Answers were Sorted based on User's Feedback
Answer / elangovan t
You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ashish
FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / aksx
how to find relay range and relay setting of three phase induction motor of 30kw ratting.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thakur
Full Load Current of Motor-52Ampas per(415.1.732.0.8)
Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)
Is This Answer Correct ? | 10 Yes | 13 No |
Answer / abhijit
as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / sanjay
40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.
Is This Answer Correct ? | 9 Yes | 26 No |
what is magnetizing and demagnetizing current in generator and motor?
How to calculate fault level of 11 KV system
why a bulb glow when connected with two end phase and neutral respectively.
it is possible to run 130V AC and 230 V AC cables run in same tray
What is GNR ? How much value of ground neutral resistance?
How to the calculating the Reactive power ( kvar )
What is switching over voltage?
What is the usega of brking resistor? and how it will useful to Drive...?
Why we use Y-Y connection in power transformer (8-10 MVA, 132 kV to 11 KV)and D-y in distribution transformer (2 MVA, 11 KV to 440 Volts)?
(1)For 3 No 1500 KVA transformer require on one single bus bar or need to be section through bus coupler means upto 3MVA.(2) 22KV Net work system as ring, How maney I/C required or 0ne I/C and one O/G.(3) What should be rating of VCB for 22 KV line.(4)Electrical/mechanical inter lock, why we need.
What are dependent sources?
how to calculate the current carrying capacity of a 25 & 16 kva distribution transformer.