Answer / elangovan t

You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span

Is This Answer Correct ?    17 Yes 2 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / ashish

FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).

Is This Answer Correct ?    4 Yes 4 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / aksx

how to find relay range and relay setting of three phase induction motor of 30kw ratting.

Is This Answer Correct ?    0 Yes 0 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / thakur

Full Load Current of Motor-52Ampas per(415.1.732.0.8)

Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)

Is This Answer Correct ?    10 Yes 13 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / abhijit

as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling

Is This Answer Correct ?    1 Yes 4 No

how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on..

Answer / sanjay

40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.

Is This Answer Correct ?    9 Yes 26 No

Post New Answer

More Electrical Engineering Interview Questions

How can we check ELCB trip current sensitivity How can we check earth resistance value

2 Answers  


What are the protective devices in a DC/AC motor starter?

1 Answers   CTS,


What is the meaning of 40X8X2 busbar dimensions for carring load of 400 Amps

0 Answers  


Why we use Capacitor in Single Phase Induction Motor?

12 Answers   IIT,


is emf is indued if dc is passed through coil

5 Answers  






what is work of choke in tube light?

4 Answers   L&T,


How much kv gas generator is needed to run 2 hp and 1 hp airconditioners, plus a refrigerator and 4 Tvs

1 Answers  


what is the pre charge circuit,what will be work which function it will be use plz tell me

0 Answers  


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

0 Answers  


When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?

0 Answers   UOM,


Why we are testing a tan delta test in transformer? which purpose conduting that test? and time priode test?

1 Answers  


How can we calculate single phase load into three phase load

2 Answers   Jindal, Tanfac,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)