how to find motor contactor rating and bimetalic relay
rating? of 30kw motor which will operate on star-delta
starter?
Answers were Sorted based on User's Feedback
Answer / elangovan t
You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ashish
FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / aksx
how to find relay range and relay setting of three phase induction motor of 30kw ratting.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thakur
Full Load Current of Motor-52Ampas per(415.1.732.0.8)
Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)
| Is This Answer Correct ? | 10 Yes | 13 No |
Answer / abhijit
as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / sanjay
40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.
| Is This Answer Correct ? | 9 Yes | 26 No |
What happens if we connect a single phase energy meter in reverse polarity.
Dear Brother can u tell the proper size selection of cable & the fault level calculation of braker, busbar etc. pls mail me at azeemk30@gmail.com
How to synchoronize the generator (with gcb,GT) to grid????? ????? from Grid iam getting power (rated 400kv/20kv) through GT and its goes to UAT.,,ST.,, now my generator(rated 20kv ) ready.,, now iam closing my GCB.,, in GT iam suddenly giving 20kv on that Gt.,, what will happend
how can we generate electricity????
what is the maximum Load capasity in LV-Panel,MDB,SMDB & Final DB'S in Electrical disribution system?
how 650 volts creates? where is use?
Is it posssible to obtain the higher speed(3000rpm) for adiferentiallly cascaded induction motors(with 8 and 6 poles)
it is clear that volts equal to the current as per ohms law. is it appliable to the AC power or only for DC. if it is appliacable to AC in transformers when voltage increases the voltage decreases ????? why??????????????
What are the application of Under voltage release?
2 Answers Techno Electric and Engineering,
please send privious years question papers of jindal steel and power ltd.My e mail id is rajanikant.sngh@gmail.com
What will be the minimum megger value of 1700 KVA Transformer? a) Do megger value varies according to climate conditions and area . b) If megger value is 100 mega ohm is it good for new transfomer. Explain?
In which iron losses is higher induction motor /transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)