how to find motor contactor rating and bimetalic relay
rating? of 30kw motor which will operate on star-delta
starter?
Answers were Sorted based on User's Feedback
Answer / elangovan t
You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ashish
FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / aksx
how to find relay range and relay setting of three phase induction motor of 30kw ratting.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thakur
Full Load Current of Motor-52Ampas per(415.1.732.0.8)
Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)
Is This Answer Correct ? | 10 Yes | 13 No |
Answer / abhijit
as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / sanjay
40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.
Is This Answer Correct ? | 9 Yes | 26 No |
How can we check ELCB trip current sensitivity How can we check earth resistance value
What are the protective devices in a DC/AC motor starter?
What is the meaning of 40X8X2 busbar dimensions for carring load of 400 Amps
Why we use Capacitor in Single Phase Induction Motor?
is emf is indued if dc is passed through coil
what is work of choke in tube light?
How much kv gas generator is needed to run 2 hp and 1 hp airconditioners, plus a refrigerator and 4 Tvs
what is the pre charge circuit,what will be work which function it will be use plz tell me
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
Why we are testing a tan delta test in transformer? which purpose conduting that test? and time priode test?
How can we calculate single phase load into three phase load