We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we
connect in common busbar&we have variable load.

Answer Posted / milinda4p

to connect 2 or more generators to a common bus those
generators should be synchronised.it means
1. frequency should be same (every generator should operate
in same frequency)
2.voltage magnitudes should be same at each bus (i:e if the
generators have different rated voltage outputs correct
transformers should be used to get the same voltages at the bus)

but the POWER RATING is not going to cause any problem for
synchronizing

But in supplying a load after connecting it is important to
adjust the power supplied according to the load.( should
maintain the frequency of the system in constant value. if
not the rotor speeds of the generators should go up or down
causing and destruction or stopping of generators )

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what are the advantages disadvantages of connecting high voltage block( 1:1 transformers) transformers between the turbo generators and busbars.

1667


i m in need of current rating chart of heavy duty pvc/xlpe, cu/al cables. can somebody provide me? if yes, plz send me at ashish_patel111@yahoo.com

1524


What are PLC leader logic program method

1265


What is the meaning of Insulation H for transformers????

1614


HOW TO CALLICULATE RESITENCE,REACTANCE AND IMPEDENCE VOLTGE OF TRANSFORMER 13.33 KVA 144/240 VOLTS 93/56 A WITH FORMULA

1523






In Indian Household, generally we receive 220V AC single phase supply. But AC has 2 phases, +ve & -ve. So in +ve half cycle current is flowing...so what happens in the -ve half cycle?? Please illustrate.

1594


RESPECCTED SIR/MADAM- I AM PRERING FOR SECTION ENGINEER (ELECTRICAL) RRB CHANDIGARH PLEASE SEND ME SOME PREVIOUS YEAR QUESTION PAPER OR MODEL PAPER.MY EXAM IS ON (30- NOVEMBER 2008).I AM VERY THANKFUL TO YOU. FROM- HARENDRA SINGH YADAV

1614


I am apply the AAI. So i want electrical sample question paper in technical with answer my id is vijayjobsmart@gmail.com

2206


How grounding is different than earthings?

717


What is the bundle conductor?

729


How could I get a certificate of competency as Electrical Supervisor? I have completed By BTech in Electrical this year(2012) for VJTI Mumbai Maharashtra. Is it compulsory to be produced while joining?

3006


why is control bus bi-directional?

1708


1. Can a 12v DC choke operate a 60v/12w PL lamp ? 2. Can a 230v ballast fire / operate a 60v/12w PL lamps.

1762


How earthing of switchgear system to be done.

1454


what is level 2 automation?

2714