Why are tertiary windings used in transformers?
Answers were Sorted based on User's Feedback
Answer / aymaan
they r used to supply the substation auxillaries at
differnt voltage levels other than primary and secondary
also when we use ynyn0 connection in transformer a delta
tertiary is used to provide closed path for 3rd harmonics
which is not there in ynyn
| Is This Answer Correct ? | 13 Yes | 2 No |
Answer / gunasekaran
this is used for auto transformer not YNyno. the following
purpose are there
1.third hormonic supression.
2.we can get another additional voltage so we can use for
auxillary.
3.reactive power compensation we can put the capacitor on
tertiary we can compensate the reactive power
| Is This Answer Correct ? | 4 Yes | 1 No |
why are use corona ring in high tension line switchgear?
mention the earthing system as per BIS?
3- What is the target from Zero Impedance, Single Phase Imp., S/C Imp. and magnetic balance tests?
what is the practical definition for voltage
What will happen if 40W and 60W Bulb is Connected in Series.
what are iron and copper losses
What is the function of a pressure Switch in a Substation?
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case
What is the difference between KW & KVA ?
the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
a solar energy installation utilizes a three phase bridge converter to feed energy into power system through a transformer of 400v/400v.the energy is collected in a bank of 400v battery and is connected to converter through a large filter choke of resistance 10ohms.1.the maximum current through the battrey will be.2.the kva rating of the input transformer is.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)