is there any difference between protection C.T and
measuring C.T?if yes then what is the difference?
Answers were Sorted based on User's Feedback
Answer / gunasekaran
protection ct is operating below the knee point voltage but
metering ct is operating almost saturation point.accuracy is
more in metering ct accuracy is not important under normal
condition. metering ct accuracy is 25%to 120% of the rated
current but protection ct is not like that suppose the ct
5P10 and 20VA burden 10times current in primary 5% error is
acceptable up to 10 times current it will feed 20VA burden
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / d.lakshmi narayana
The difference of protection ct & measuring ct is the
protection ct secondary current is very accuracy .Ex 600/1A
ct is the sec current is Exactly coming 1A But metering ct
is not accuracy That same ct is coming Sec current is
0.98--0.97 A
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / ahir ashish
protection ct is depand upon the ratio error and measureing
ct is depand upon phase angle error.
| Is This Answer Correct ? | 2 Yes | 4 No |
What is meant by earthhing of a magnetic flow meter and when to use empty pipe detection?
How shall i select the value of capacitor or inductor in a system?
what is mean by derating factor?
formula for cable size calculation for current?
10 Answers KL Power, ONGC, RL Clean Power Pvt Ltd RLCPPL, SAS, Sobha Developers,
how much up to LT Voltage range?
What is grid collapse? what is the reason for it?
why are use corona ring in high tension line switchgear?
we have one ups its neutral is not earthed.its one distribution MCB has a earth fault.but we can not put off any MCB.so how to find out that in which circuit is earthed without isolating the breaker.
HOW TO CUT A CAKE IN 8 PIECES IN 1 STROKE
when transformer oil should be filtered/tested?
how oil in the MOCB was reduced compared with OCB? what are the features of the MOCB?
0 Answers Asahi, BARC, K-Electric,
i need to calculate high voltage line power factor daily basics but there is meter reading kwh and kvah while calculating power factor kwh/kvah formula was right. for examble there is point c=13kwh c=1.8 lag c=1.2 lead and c=14.5kvah like that i know that p.f =kwh/kvah but c=1.8lag kvarh and c=1.2lead kvarh points i dont know if u know please reply
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)