Can we use generator transformer as step down transformer?
How?
Answers were Sorted based on User's Feedback
Answer / atif rasheed khan
there are two cases arises here, in first case our answer
will be yes under the following condition.
the generator should be so excited till its voltages
produced be equal to the previous step up voltages done
through transformer, however these rise in voltages are just
restricted to 33KV, because beyond this voltage level there
arises a critical issue of the winding insulation.
in this method just reverse the connections, i-e change the
L.T as sending voltage side, and the H.T as generation side.
however in the second case , our answer will be no, if
higher voltage step up transformer are used, due to the
above mentioned problem of insulation of transformer.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
We have to back-charge UGT if the synch is done at generator
output and may be for aux supply
| Is This Answer Correct ? | 0 Yes | 0 No |
Yes. If the aux tr is connected to GT and there is no generation ,the GT is back charged with grid duly isolating gen, for aux supply .
| Is This Answer Correct ? | 0 Yes | 0 No |
a 440v 60hz 03 phase 100kw generator can deliver how much power in kw for 220v 60hz 01 phase load?
what is difference between earth fault& restricted earth fault.
why ups in kva ratings?
What is the function of auadag in a cro?
to transmit 30kw of power at 30 km what is voltage required
2 Answers Anglo Eastern, Merchant Navy, NPCIL,
hi all i like to know vat is power plot in control systems also i want to know abt latest trends in electrical & electronics
We have two parts in generator, electrical & mechanical. how it works?
What is meant by "tampering detection" of a electrical energy meter?
kindly tell me how the load on generator increase by just increasing the fuel of prime mover, as if for exampple 20 MW gen set is synchronized the load ramps from zero to 20 MW gradully and during this procress only fuel of prime mover increases. Which thing determines the load on generator with respect to fuel
What is difference between metal clad & metal enclosed switchgear?
which type of motor we are using in local train???
4 Answers Asia MotorWorks AMW,
1. alternator has full load regulation of 4% when pf of the load is 0.8 lag, 1500 rpm. full load regulation of 1400 rpm for 0.8lag will be ________ ?? 2. torque angle of a sync m/c operating from a constt voltage bus is usually defined as space angle between _______ . 3. method most effective in finding out no load losses in large DC shunt motoris ______ . 4. current carrying capacity of fuse material depends on ______ . 5. coil has res. 10 ohm, inductance 1H. what wil be current after 0.1sec after switching on to a 500V DC SUPPL ? ? 6. effect of phase lag compensation on servo systems ___________ . 7. rotor of a dc machine is usually supported upon ______ . 8. DC motor is preferred to AC motor in which application ?? 9. 3 nos of 10:1 Xmer are connected in Star-Delta to supply a load at 230V.the supply voltage must be ______ . 10. voltage source produces max current in which circuit. 11. cal. power, if current and voltage are out of phase by 90 degree. 12. suitable length of Xmission line of power at 66 KV. 13. Which of the theorm helps in simple computation when the load across a ckt is varying ?? 14. what is the adopted line length for power Xmission of power by cables ??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)