HOW TO CALCULATE EHV CABLE SIZING?
Answers were Sorted based on User's Feedback
Answer / ram
Use manufacturer table.
1st step:Calculate the FLC.
2nd:Calculate the Voltage drop.( If It is more than 5%)
chose higher size.
3rd step:Calculate fault Current for the system and see
cable short circuit withstand.
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / hanumantha reddy
i belive this is currect thank you for your information
| Is This Answer Correct ? | 2 Yes | 2 No |
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
wat is d first thing to be seen 2 lay a cable in a particular area??
what do u understand about FACTS? how they are useful?
enlist types of dc generator
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
only some transformers and some generator requires NGR why?
Why do we choose 33kV transmission for industrial purpose and 11Kv for township?
What is the knee point of voltage of CT?
At what condition differential relay will act in transformer and ht motor?
advantages of vvvf drives over non vvvf drives for EOT cranes
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.
how to select energy meter? have any calculation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)