Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why we r used APFC Panel in industrial area.when P.F. low
then wat will be the effect in our system?

Answers were Sorted based on User's Feedback



why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / ganesan govarthinam

when power factor is unity,then industries receive active
power or useful power only i.e KW=KVA
If it is lagging PF,the industries receive both useful power
(KW) and reactive power(useless power)(KVAr).To meet this
reactive power, distribution transformer capacity also to
be increased.Then only we can avoid low voltage,losses
etc.
So we have to provide APFC panel to bring the pf to unity

Is This Answer Correct ?    55 Yes 4 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / rajeev

APFC Panel is used to maintain the power factor near unity
by adding capacitance across the load.
P = V x I x Power factor.
100 = 100 x 1 x 1 ( Idle case)
If power factor decrease to 0.1
100 = 100 x 10 x 0.1

Here we can observe that current in circuit increased
from 1 amp to 10 amp with decrease in power factor from 1
to 0.1

This is the effect of low power factor in system. Due to
this increased current higher rating of cables , breakers
etc required. also due to this increased current we require
more power generated as MVA demand shoots up.

Is This Answer Correct ?    31 Yes 3 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / surender singh

In industrial area's due to inductive loads the power factor
becomes low. As the PF low, the inductive power also becomes
low.To raise the power we use APFC Panel.

Is This Answer Correct ?    25 Yes 9 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / umashankar

The ideal Power Factor (PF) is Unity or 1, but most
Industrial loads have a PF lower than 1. Moreover, this
lower PF is usually due to Inductive loads, arising out of
the windings of Transformers, Motors,etc. These loads
consume kVARs (the Wattless component) from the supply
line. The APFC supplies these kVARs via a capacitor located
close to the load, reducing the current drawn from the
supply line. For an Industry with dynamically changing
loads, Automatic PF Compensation affords the best Return on
Investment, since the kVAR investment required is smaller
than with fixed capacitors needed to meet the entire load.

Is This Answer Correct ?    17 Yes 2 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / kirti harinkhede

In industry most of the load is inductive in nature which
results in lagging power factor that is why there is loss
and wastage of energy which results in high power bills and
heavy penalties from electricity boards. If the load is
uneven it is very difficult to maintain unity power factor.
To overcome this difficulty APFC panel is used which
maintains unity P.F.

Is This Answer Correct ?    5 Yes 0 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / sunil.dutta

lower Power factor,s harms every one knows, but we use a
capacitor panel to confirm our p.f. not crossing limits
causing government penalty on lower p.f of plant.

Is This Answer Correct ?    5 Yes 2 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / gautam makavana

What is the function of reactor in LT &HT Apfc panel ? And why it is used ?

Is This Answer Correct ?    2 Yes 1 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / ramendra shukla

Automatic power factor correction Panels are used in
Industry for maintaining the power factor close by unity &
for reducing Reactive power component by the auto
functioning(with solid state device) of Capacitor Banks.
and by getting the Pf close to unit we will also get the
incentive(as per respective PF slab) from Energy providing
co.
In case of low pf it means the current is lagging behind
with voltage and we are having the reactive power in
syatem.So system will take more active than earlier.

Is This Answer Correct ?    2 Yes 2 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / vivek

if we increase the pf as unity we get healthy power and no harmonic present ion that system. so that losses is decreses and our equipment runs up to full efficiency. so that we reduce the tarrif.and finally save electricity save money..

Is This Answer Correct ?    1 Yes 1 No

why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our syste..

Answer / gunasekaran

kva=kw+kvar
apparant power is constant because our TR rating we cannot
alter so if KVAR is incress active power is decress so we
cannot use power for useful for that at the same time for
low PF it draw more currrent so we have to design the
appaliences for higher rating.

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

What will happen if supply to three phase motor is given wiyhout inerting rotor in it?How much current it will draw?

5 Answers  


What does impedance in the windings of transformer signify.

2 Answers   Johnson Controls,


Which element is highly conducting coppoer or gold?

3 Answers  


There is two transformers of 2MVA & 3MVA, which transformer is located at the sending end & which is at receiving end. why?

3 Answers  


when we gave dc supply to 220v dc motor its rpm is 1200. then we gave 180v. how many rpm of its motor. gave answer with calculation at my ID.... ravizak@ymail.com

0 Answers   Godrej,


in how many ways we can make induction motor to run in reverse direction?

5 Answers  


can any one suggest paper presentation topies for electrical engg?

0 Answers  


Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT? 

0 Answers  


What is the phase relationship between the primary and secondary voltages of a transformer?

0 Answers  


Plugging is a phenomenon to= A braking the motor B to accelerate the motor C to run IM as generator D to start the motor

0 Answers  


When placed close together, two positively charged materials will

1 Answers  


What is meant by impedance? difference between high & low impedance ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)