WHEN BOTH WIRES OF THERMOCOUPLE R SHORTED WHAT IS THE OUTPUT
THE TEMP ARE 0,30,250,320
Answers were Sorted based on User's Feedback
Answer / khalid javed
it will give the atmospheric temperature.and temperature
will 30
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / gopalakirshnan
when both wire short means it shows ambieant temp. or 30c
| Is This Answer Correct ? | 7 Yes | 0 No |
your question is not clear please specify how they are connected
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / vinesh prajapati
it will give the atmospheric temperature.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / saber
If both wires of thermocouple are shorted then the output of
thermocouple will be 0 mv. The question is quite confusing.
On the other hand both wires of thermocouple reader are
shorted or connected in a shorted circuit thermocouple then
it will show ambient temp.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / akhilantivirus
Detecting open thermocouples easily and quickly is especially critical in systems with numerous channels. Thermocouples tend to break or increase in resistance when exposed to vibration, poor handling, and long service time. A simple open thermocouple detection circuit comprises a small capacitor placed across the thermocouple leads and driven with a low level current. The low impedance of the intact thermocouple presents a virtual short circuit across the capacitor so it cannot charge. But when a thermocouple opens or significantly changes resistance, the capacitor charges and drives the input to one of the voltage rails, which positively indicates a defective thermocouple.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is interlock system and why we use of this?
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
should I use Hydrostatic Pressure Transmitter for measurement of DENSITY of filled tank ? If YES then please explain how.
It is desired to reduce effect of 50Hz pick up in a thermocouple measurement. If a third order LP filter is used for this, what should be its cut off frequency, if gain should be 0.001 at 50Hz.
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
How to Calibrate Flow Switch in field
if temperature transmitter is showing wran. sensor 2 fail how can you remove from the transmitter display m/n.3144p rosemount
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
loop chech tools list
What is TMR
what pressure transmitter?
how u calculate ai/di/ao/do capacity in ur dcs?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)