if we want to increase the back up time of an UPS what
should we do ?
if we want to decrease the charging time of a
battery/batteries attached with the UPS what should we do ?
Answers were Sorted based on User's Feedback
To increase the back up of an UPS one needs to have higher AH
Rated battery.
Is This Answer Correct ? | 14 Yes | 4 No |
Answer / khaleeq us salam
if we want to increase the charging of a battery first we
have to make sure that the battery have enough AH. then we
should know that there is a internal circuit in a UPS. we
can increase the charging time of a battery through that
circuit.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / jayaraj
You have to increase the AH of the battery. Make sure that the charger of the UPS have enough capacity to charge the batteries.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / nayan
if we attached another battery with ups then then the backup
time increased or if we attached a higher AH battery then
backup time increased. but if battery is higher AH that time
may be another charge controller assigned to reduce time of
charging and prevent the damage of UPS.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ram
If changing hardware is a constraint then UPS battery time
can improved by reducing the load connected to the ups !..
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manoj
Ups- back can be increase by increasing the AH capacity of
battery or by increasing no. of battery unit.
Before doing so we need to syncronise it with Battery
charger/Rectifier.
Is This Answer Correct ? | 1 Yes | 2 No |
what is recovery voltage & transient voltage ?
What is the difference b/w earthing & grounding?
what is recommended breakdown voltage of transformer oil?
for a 500 KVA connected load, I calculated 30% of capactor for power correction. Even after using 225 KVR capactor PF is not improving. What could be reason for low Phase correction factor?
In 3pin or 5pin socket why the earth pin is bigger
why we setting 95 deg and 105 deg in wti and oti of distibution transformer ? give the reson for that ?
what is bus PT ?
Is reverse power relay of generator operate due to voltage variation problem? please clearify.
For DG or Transformer body earthing, is it necessary to terminate the earth bus to earth pit directly? If not terminated to earth pit directly in earth pit and connected to any common bus strip which ultimately connects to earth pit, what will be the pros and cons?
super position theorem is applicable to
how can i improve the power factor in domestic (230v)
How the main bus bar rating of 400kV switchyard with one and half breaker scheme is calculated.