what is %impedanece
Answers were Sorted based on User's Feedback
percentage impedance is voltage drop on full load due to
winding resistance and leakage reactance
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sangeetha.np
The percentage represents the amount of normal rated
primary voltage which must be applied to the transformer to
produce full rated load current when the secondary winding
is short circuited. The maximum short circuit current that
can be obtained from the output of the transformer is
limited by the impedance of the transformer and is
determined by the multiplying the reciprocal of the
impedance timed the full load current . Thus, if a
transformer has 5% impedance, the reciprocal of .05 is 20
and maximum short circuit current is 20 times the full load
current.
| Is This Answer Correct ? | 4 Yes | 2 No |
Relation between magnetic field strenght and magnetic induction is a) Voltage b) current c) Speed d) tarque
what is star&delta connections?
At what voltage domestic tubelight works?
how to select cable size for three phase?
What is the different between conventional MCC and intelligent MCC? Common controller or controller for each bucket
How can calculate HT side VCB? For example I have 1250 KVA load what will be HT side VCB Amp.range and what size XLPE cable I use for HT side.
2 Answers NASSA, Orchid, SB Automation,
where the lexical paramater will use in fron end?
Are Refrigerators & Deep Freezers the Inductive load ? How to calculate the Power Factor & hence the Output Power for them ?
What do you mean by Transformer?
9 Answers Hyundai, NTPC, wbsedcl,
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
Hello Can I use step up HV transformer 440/4160V as a step down? Thanks Evgeny
During the transients in alternator,the mechanical power input remains almost constant while the electrical power output changes significantly.Why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)