What is the Difference Between the SCADA & PLC ?
Both it also control and Supervise Then what Special in
Scada & PLC?
Answer / niyaj
PLC is a control device .It Should not monitoring the
process.and SCADA is graphical monitoring device it should
not process any control activities.SCADA interface with PLC
for real time Control & Monitoring purpose.
Is This Answer Correct ? | 10 Yes | 0 No |
Why we use CT on differant phases of 2ph.PT detection for brush-less static excitation of 3ph.,400v Synchronous Generator? What happen if use CT on same one of VT phase?
A.V.R maintains the voltage of a generator when it is in island mode but when the generator is synchronised with grid it maintenance the P.F,how it happens please any body explain it in detail.
How earth resistance reduses by pouring water coal and salt?
Please specify the parts of VCB&ACB
Factory acceptance test. FAT. For 132 kv transmisstion towers what is that meaning and what are the tests commonly companies perform now days.
What is the reason of using bus-bars on the secondary on the LT transformers?
For 160kw motor what size of cable and material is needed.?
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
In a star-star connected h.t transformer why we use NGR on the secondary (l.t)side.
what is d check in dg 1500kva
How we can calculate the life of Lead acid battery
What is the type of feedback used in an op- amp schmitt trigger?