how manys ways dp transmitter can be calibrated having
range of -150 to 400mmwc,what side pressure u will apply?
Answers were Sorted based on User's Feedback
Answer / basil
TWO WAYS.WE WANT TO GIVE 150 MMWC ON THE LOWER SIDE AND
ZERO PRESSURE ON HIGHER SIDE AND SHOULD GET THE OUT PUT OF
4 mA.AND ZERO PRESSURE ON THE SIDE OF LOWER AND 400 mmWC ON
THE HIGHER SIDE AND SHOULD GET THE OUT PUT OF 20mA.
IF NO PRESSURE ON BOTH SIDES THE OUTPUT SHOULD BE 8.36 mA
(IF IT IS A 4-20mA TRANSMITTER)
| Is This Answer Correct ? | 21 Yes | 2 No |
Answer / naresh makhwani
We always have to apply pressure on the high side of the
transmitter. You cannot apply pressure on the lower side,
though if you will apply it gives you the negative reading.
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / jigar anadkat
You Can Calibrate in Two different Ways:
1) By applying normal pressure according to the range i.e.
(-150) mmwc with vacuum pump and observe 4 mA and keeping
this pressure on LP side apply 400 mmwc in HP side and
observe 20 mA (in steps).
2) Apply 150 mmwc on LP side and observe 4 ma [HP-LP=0-150
= (-150 )], then keep LP side open 0 mmwc and create
550mmwc (400+150) span by applying pressure on HP side and
observe 20 mA (in steps). If no pressure on both the side
your TX will give o/p = 8.36 mA
| Is This Answer Correct ? | 2 Yes | 1 No |
A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic meter/hr. Thorough impulse line flushing and zero calibration has been done, yet problem persists. What do you think is the problem and how do you rectify this fault?
The performance of a pump is monitored by measuring the ________ and _________ pressures
whether radar level transmitter is applicable for the open tank
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
what is electric motorised valve working principle.
What is the purpose of MATLAB?
how u calculate ai/di/ao/do capacity in ur dcs?
WHAT IS THE DIFFERENCE BETWEEN PLC AND DCS
55 Answers ABB, Adani, Adani Power, GMR, IIUC,
Q-Explain the different load conditions that will produced different offset which may or may not be acceptable to thhe control function
My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
What are the advantages and benefits of using PLCs to automate a section of a plant?
How digital input and digital output 's are working in dcs
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)