Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Y to use 4 to 20ma instead of 0-10v

Answers were Sorted based on User's Feedback



Y to use 4 to 20ma instead of 0-10v..

Answer / ravinder

Because Voltage drops as resistance of cable conductor
increases but current will be same at any point of the
loop.4mA is called Live Zero,shows liveliness of the loop
when process variable is zero.

Is This Answer Correct ?    27 Yes 4 No

Y to use 4 to 20ma instead of 0-10v..

Answer / jaldeep

For signal transmission we are using 4 to 20 mA, because of
following reasons.
1. If you are using 0 to 10 for long distance then
signal will be dropped due to cable resistance you will not
get correct feedback
2. 4 to 20 mA will give correct feedback even for
long distance. It will not drop according to cable
resistance. Only you have to keep loop impedance as per
your field instrument.
3. Open loop, you can easily detect in 4 to 20 mA.
You can program if mA is less than 4 then you can define it
as open loop.
4. For 0 to 10 v input if cable is open then it will
be difficult to identify that cable is open or input is 0
volt.

Is This Answer Correct ?    17 Yes 0 No

Y to use 4 to 20ma instead of 0-10v..

Answer / himanshu

beacause total loop resistence is 250ohms.
so 24VDC supplied loop 1v corresponds to 4mA
and 5v corresponds to 20mA.
HART PC communicates to 1-5VDC only.
As explained in above answer 4mA is LIVE ZERo.
for 20mA reason is above 20mA current can be hazareous for
fieled.(fire).like HC and Refineries
thats why 20mA signal is used.

Is This Answer Correct ?    9 Yes 4 No

Y to use 4 to 20ma instead of 0-10v..

Answer / ecxlsync

current signal is used because as explained
it will not change even the loop resistance is changed
due to transmission lines resistance. it is stated in the KCL that current entering in the circuit will be equal to the
current leaving no matter if the circuit resistance is changed.

Voltage signal is greatly affected by the circuit resistance.
long distance transmission has large wire resistance that
will cause large voltage drop.

Is This Answer Correct ?    1 Yes 0 No

Y to use 4 to 20ma instead of 0-10v..

Answer / kalpesh

Because if we use 0-10V signal and if there is a break in
cable loop then it will show 0V which is the low level of
the measured signal but in reality it is a signal failure
from transmitter.

Is This Answer Correct ?    4 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

If I installed wrong directions orifice plate then what showing value d.p transmitter?

2 Answers   Forbes, STS,


i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500 ltr/hr.) what should i do?

9 Answers  


What is zone,loop/fire alarm system?

0 Answers   Emco,


How EMF is generated in Thermocouple

3 Answers  


Square root calculation for dp flow transmitter?

0 Answers  


1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling

0 Answers   BARC,


what is the zero and span trim?

2 Answers  


1. what is modbus cable? 2. what kind of communication we are using for the interface of DCS, ESD and Third party cabinets? 3. What is serial communication and peer to peer communication?

0 Answers  


Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?

2 Answers  


Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?

0 Answers  


What is the difference between DCS and SCADA?

1 Answers  


draw a loop drawing of vibration beginning to end

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)