why ht motor connection in star
Answers were Sorted based on User's Feedback
Answer / avdhesh
HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.
| Is This Answer Correct ? | 86 Yes | 1 No |
Answer / anand
Ht motor star connection current is root 3 times low carried & power saving but delta connection current is high
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / svrao
HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / narayanaswamy
I am of the opinion that star connection of HT motor is done to have better operation of protective gear
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pankaj gajare
Because HT motor having large starting current so that if
your connection will be in star then your current will be
root three so its automatically reduce.
its star delta principle...in star connection current will
root three times reduce.
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / jameel
the ht motor connection in star because it is easy and
cheaper than delta connection in high voltage and star
delta connection not used in this system .
and the best question here why the ht capacitor of power
factor connection star not delta although the delta
connection is more economecal than star. we need in star
three times farad(reactive power) of ccapacitor than delta
but we connection star not delta because the same reason in
ht motor.
but the ht transformer some times it is necssary to
conection the primary or the secondary or both delta
accrding to the requirment of network.
| Is This Answer Correct ? | 2 Yes | 9 No |
Answer / priti
in star connected sysytms...u can provide it with a
neutral..so that in case of faults the fault current will
flow through the neural nd hence preventing shocks!!
| Is This Answer Correct ? | 1 Yes | 9 No |
HOW CAN I GET 5CORE HO7 CABLE SIZE IF I HAVE 1800A?
what is meant by 3rd hormonics ?
How to calulate the NGR resistance ?
how to set the overload setting in the thermal overload relay?? is there any calculation in that??
How to parallel a alternator without using synchro scope or lamp methods
If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.
Why HT cable have only 3 core ?
I have 320 Kva DG Set his KWh running is 77 , how i can calculate into electrical unit .
2 Answers Anuj Enterprises, Schneider,
HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?
12 Answers Al-Malik, All Star Electric, GEC, Reliance, Universal Industries,
how is the leakage current flow only through guard wire (when guard wire is connected in the circuit)????
Upload data by LSMW via BAPI in SAP system.
How can I calculate the trnaformer effciency at different loading condition?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)