how to set the overload setting in the thermal overload
relay?? is there any calculation in that??
Answers were Sorted based on User's Feedback
Answer / elango k
it is based on the charaterstic of olr
100% to flc can be set it is normal
85% to flc can be set it is sharp
because an olr starts to work 115% of flc
for eg. if a motors flc is 100 amps
i am setting 85amps , the olr starts to work
at 100amps it trips the motor
Is This Answer Correct ? | 13 Yes | 6 No |
Answer / balasubramaniyan.t
Overload setting in the thermal overload relay to be done based on the motor full load current.The setting current of the relay should not exceed the motor FLC.
Is This Answer Correct ? | 12 Yes | 7 No |
Answer / veerendra
the overload relay setting is donr based on the value of
line current of the motor..
first calculate the line current & set the elay for the same..
Is This Answer Correct ? | 4 Yes | 9 No |
It is advisable 2 use auto-transformer if transformation ratio is-a)110KV/11KV,b)230kv/110kv,c)110kv/66kv,d) 400kv/230kv
Sir i completed diploma in electrical from govt. Polytechnic dhanbad (jharkhand) . In 2012 . Now i am working in sail iisco plant . Sir i want to get electrical supervisory certificate for applying in ongc . From where i get this certificate please guide me procedure step by step
How to take Transformer oil Break down voltage test?
what is feeder bay?
if the transformer at full load have a iron loss =900w and copper loss = 1600w . what percent of the load will the transformer has a maximum efficiency?
What is the use of oil in transformers?
Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB
How i can select current transformer and meters for the upgrading the panal..for 200kw to 600kw....i need to select monitoring and protection ct,s and apmpire meter ,kw meter too.
while doing high voltage test on 11kv/433 distribution transformer why we only give 28 kv on hv side and 3kv on lv side for power transformers what is the value what factors it depends
why impedance test in power cables?
how electrical energy is converted into mechanical energy in dc motor
what is power