how to set the overload setting in the thermal overload
relay?? is there any calculation in that??
Answers were Sorted based on User's Feedback
Answer / elango k
it is based on the charaterstic of olr
100% to flc can be set it is normal
85% to flc can be set it is sharp
because an olr starts to work 115% of flc
for eg. if a motors flc is 100 amps
i am setting 85amps , the olr starts to work
at 100amps it trips the motor
Is This Answer Correct ? | 13 Yes | 6 No |
Answer / balasubramaniyan.t
Overload setting in the thermal overload relay to be done based on the motor full load current.The setting current of the relay should not exceed the motor FLC.
Is This Answer Correct ? | 12 Yes | 7 No |
Answer / veerendra
the overload relay setting is donr based on the value of
line current of the motor..
first calculate the line current & set the elay for the same..
Is This Answer Correct ? | 4 Yes | 9 No |
What is the RMS and DFT principle of analogue maesurments. Which way they are advangages. where which princples give optimum results.
what is form factor?
What is the safety factor is to be consider while selecting the switchgear and protection for electrical system
WHAT HAPPENS IN DIFFERENTIAL PROTECTION IF CT REACHES ITS KNEE VOLTAGE POINT?
how to calculate the cable size in sqmm if load (kw) is given?
HOW DO YOU CAN CHECK A 15KV DIODE, WHETHER IT IS OK OR NOT?
How to convert 2 phase to 3 phase electricpower in induction moter?
One 15kw motor Why we used star delta feeder?why not used DOL please explain in details
3 Answers BMM Ispat, GSK, Pitti Laminations,
What do you mean by Transformer?
9 Answers Hyundai, NTPC, wbsedcl,
WHAT IS MEANT BY INSULATION CLEARANCE IN VACCUM?
Do you know how to connect a motor of different H.Ps?
How to solve the problem of low voltage at consumer end in distribution system if one phase come low voltage of transformer