We have ZR22G-100-S-A-E-T-T--E-A/CV/F1 Model Zirconia
Oxygen analyser which is Yokogawa make. I kept the analyser
in Flue gas path at Air pre heater area. My plant is 7.5MW
Biomass power plant. For a particular fuel, Coconut Husk
which contains Sodium and Potassium chlorides iam not
getting proper reading, Analyser output always Zero. I
calibrated the analyser and it is OK. For Other fuels like
Wood chips, Cholam waste, DOB, Groundnutshells, Ply wood
waste and all iam getting actual percentage of Oxygen. What
is the main reason behind this draw back?
Answers were Sorted based on User's Feedback
Answer / tarique
please check your heater which is used in zirconia
change your load air percentage in firing and observe
changing or not if changing means actual is zero
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / haresh mod
Pls. set your fuel temperature bcs. normally zirconia o2 analyzer work on 800-900 deg. centigrade temperature.
So set the temp. still you not get result then pls regulate your flow and also with your process gas you have to ptovide atmospheric air with set pressure(>=1kg/cm2).
| Is This Answer Correct ? | 5 Yes | 0 No |
1. what is 3 point calibration & 5 point calibration? 2. If we use hart communicator to set the LRV & URV of a smart transmitter, did we calibrate the transmitter? why? 3. Make a complet list if meterials needed to properly connect a pressure gauge to a steam pipe using 1/2 inch stainless steel tubing. The gauge connections is 1/2 inch NPT-M and the steam pipe tap has a 1/2 inch female coupling, compression fittings are use. 4. What are the tools in loop checking? 5. What would the ISA symbol of a square root extractor look like? 6. What would you do to completely prepare for the configuration? 7. What safety measures must you undertake when doing configuration? 8. what are the two most commonly use programming languages used when we configure a PLC? 9. What would you do if you accidentally skipped a step in the configuration procedure? 10. How would you know if the configuration were sucessful? 11. Name at least 3 selections available when we configure the burnout protection of a controller?
3 Answers EI Electrotechnical Institute,
what are the steps to follow force a particular input or out put from ics triplex esd system?
what is thermopile?
Can anyone send most commonly asked interview question in Oil & Gas industry
how can i calibrate I/P converter
What is the principle of capacitance type level transmitter?
how to check earthing,what is minum ohms for proper earthing
what is cavitation in control valve? & how we can avoid it?
1 Answers Forbes Marshall, Reliance,
Why Flow measure in Square-root?
I work on a electronic positioner transmitter 4211 at the field.I connect my multimeter in series to get the current output then I calibrate it to 4ma in 0% of position of the valve and 20ma in 100% position of the valve.My problem is in the field I get the correct output current based on my multimeter but in the dcs they only receive 40% in a output 20ma of this positioner.Then I try to simulate in this analog card and they receive the equivalent percent on the value that I simulated.Is ther any possibility to reset the zero and span of this positioner 4211 fisher.And what other possibility I can do to fixed this.This is my email add ( landicho_randy@yahoo.com )
Yokogawa dcs nodes advantages?
why flow transmitter showing 2.2ma?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)